CPU did n't give the output,Istack message enclosed

kareemmm

Member
Join Date
Aug 2007
Location
KSA
Posts
14
Now we are facing a problem that our S5-115U is not working proper Last time we have a power failure in our plant and when restart the plant I saw in the plc message that battery low. I replaced the battery and energize plc. But it didn't give the out put. So I reload the program again but I can't cold start the plc, Then I use the trouble shoot using our SIEMENS FIELD PROGRAMMER and the following are the ISTACK messages I request pls. give the solution and what may the problem

SIEMENS SIMATIC S5 PS 3A 115U CPU 942B DIGITAL INPUT

32 X DC 24V 3CARDS

DIGITAL OUTPUT

32 X DC 24V 4CARDS

 
The ISTACK second page tells you why it crashed, but it needs to start and crash to get that page. The info you have shown just tells us the make-up of the PLC.

I'd try an overall reset of the CPU and then run the PLC to ensure it can run empty. Then stop and reload.
 

Similar Topics

Now we are facing a problem that our S5-115U is not working proper Last time we have a power failure in our plant and when restart the plant I saw...
Replies
13
Views
4,179
I have a 90/30 CPU331. I am trying to upload the program out of the CPU and keep getting an error uploading the logic. Error 8262: Error...
Replies
6
Views
103
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
189
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
Replies
7
Views
184
Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
Replies
1
Views
79
Back
Top Bottom