The fault light, if solid, generally indicates a hardware failure. If blinking usually indicates a problem with the application. To get any more specific requires numbers only obtainable by hooking up the programming software and reading the specific fault. Then more detailed advice can be given. Your question is a little like 'my car stopped, what's wrong?'
Cycling the power (rebooting) the PLC might handle it. Depends on what the fault is and what caused it. I had one fixed PLC that did this periodically. Always had to re-download the program to it. Then I added an EEPROM and programmed it to load from the EEPROM at each cycling of the power. (Only cycled the power when the CPU faulted out. The problem progressively got worse though. Come to find out, a capacitor or 2 on the powersupply (built into the fixed processor) had become desoldered from the circuit card, which must have been causing surges.
Another thing I recently did, was to do some math instructions, which caused math over flows, which caused the CPU faults. This was in a project, I was working on, off to the side, and basically, I did it on purpose.
Some CPU faults can only be reset if you have the SLC500 programming software. If such is the case and the program is not lost in the PLC, should be able to go online and see what caused the error. This would be found in the processor status, under the errors tab. With out the programming software and/or a backup copy of the application, you might be in trouble.
If you have a SLC 5/03, 5/04 or 5/05 you can change the keyswitch to program, then back to run. This will clear a fault and resume the program. If you have RSLogix 500 or know someone who does I recommend connecting to the PLC and finding out why it faulted by checking the fault code.
SLC 5/01 CPU Fault light Flashes, get on-line and it is a Major Error Halt S:1/3=1 Module (CPU) in slot 0 Wrong Type for User Program. Major Error...
19,934
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,016
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,801
Hello intelligent people, I hope you guys can help me I currently have a problem with a telemecanique TSX 17 plc The plc was cut off power supply...
2,792
We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and...
21
4,174