I have CPU314C-2 PN/DP, with 4 channels integrated Analog input that I need them for my project, I am recieving analog signal from weighing indicators ( I can choose 4-20mA or 0-10V), at the same time I am using Portal Step7 V11 for programming the the S7-300 CPU314C-2 PN/DP , I made the correct wiring for I and V also the hardware configuration for the analog inputs also I have tried both I & V from the hardware configuration but I can not receive the analog value from the input tags!!! I have tried a loto_Oo_Oo_O, any one could help me if I forgot something will be very appreciated.
thanks and best regards
If you use the addresses suggested by the system defaults, then you should be able to load the analog values like this:
Put this on OB1:
//1st integrated analog input
L PIW800
T MW100
//2nd integrated analog input
L PIW802
T MW102
//3rd integrated analog input
L PIW804
T MW104
etc.
Have you done like that ?
thanks Jesper, you are right the problem I was using IW800 instead PIW800, now it is working just like you recommended.
thanks again for your support(y)
I am receiving the following error message on the Simatic OP17 $545 DB 32b 41 3 not avail. Before the restart that this HMI always does...
20
6,233
Hi i have Cpu314c-2dp in hardware. i want to monitor tags in wincc 6.2 with profibus interface. but in netpro when i want to insert connection...
1,176
Hello, guys! I have something wrong with my CPU314C-2DP. The situation is: 1. After 30 min working-time all CPU LEDs became fast-blinking. 2. I...
1,325
how should i network 20 s7's? i was going to use some mpi-lan converters like these. http://www.process-informatik.de/produkte/s7-lan&lang=en_ is...
1,887
Hello. Can anyone please tell me, if my Siemens cpu314C-2PtP is able to communicate with socalled I2C ? I have this 24Vdc motordrive, that I...
4,431