CTC Parker P1 touch screen display

egist

Member
Join Date
Jan 2008
Location
Kent, WA
Posts
2
P11-314DR touch screen displays the upper left corner of the Interact software as if it is identified as a much bigger screen.
Can't figure out what to change. Help!
 
The P11 is a quarter VGA screen. When it boots up, you will only see a quarter of the full DOS screen. However, once interact and your project load, you should see the whole screen. Unless your project is designed as full screen, then it will not scale down to the quarter size HMI.

Are you creating a project or trying to get something you already have to work?
 
A very common problem.

In the Project tree, highlight the Application Manager Folder, then Settings menu:Application, then General tab and select resolution (320x240.
 
P1 display problem solved

Yes! I checked the Interact Application Settings. I had set the screen resolution to 320x240 but the Start Up Mode box was hung up in Program Mode. After toggling between screen resolutions the Start Up Mode set itself to run for the 320x240 selection.

Everything is fine now. Thank you for the help.
 

Similar Topics

I installed a new Direct Soft 205 Series/240 PLC in a CTC Turret. The turret uses an interactive CTC/Parker touch screen. After installing the...
Replies
0
Views
2,414
Hello!:confused: One of our clients is having a some problems with a touch screen CTC-Parker P11-314DR, he says he can't access to his HMI...
Replies
3
Views
5,877
Hi all, A client of us have a problem with a Parker XPR06VT-2P3 6" touch screen. He says that the central area of the screen is not responding to...
Replies
4
Views
9,382
Hello everyone, I have a quick question. We are builing a system utilizing a compumotor 6K and an Omron PLC. A touchscreen is required for this...
Replies
3
Views
6,438
Hi, I have an old unit HMI with model PA10T-133 (PA Powerstations series). 1. I just have an inquiry whether which particular software to use...
Replies
1
Views
1,842
Back
Top Bottom