tjabadie Member T Join Date May 2012 Location LA Posts 1 Aug 10, 2012 #1 need communications setup for siemens mp377 to talk to a cti 2500 via rs422, anyone done this?
JesperMP Lifetime Supporting Member + Moderator Join Date Feb 2003 Location ᚴᚬᛒᛅᚾᚼᚬᚠᚾ Posts 16,342 Aug 10, 2012 #2 Is a CTI 2500 similar to a TI 505 PLC ? If so, you can chose the driver "Simatic 500/505 serial" in WinCC Flexible.
Is a CTI 2500 similar to a TI 505 PLC ? If so, you can chose the driver "Simatic 500/505 serial" in WinCC Flexible.
Ken Moore Lifetime Supporting Member Join Date May 2004 Location North, West, South Carolina Posts 3,477 Aug 11, 2012 #3 CTI 2500 PLC's "speak" the same protocol as the TI505 PLC, so the same driver should work. The baud rate for the serial port is set with dip switches on the CPU board. I think you will have to pull the processor to access the switches.
CTI 2500 PLC's "speak" the same protocol as the TI505 PLC, so the same driver should work. The baud rate for the serial port is set with dip switches on the CPU board. I think you will have to pull the processor to access the switches.