Hi all,
I have been allocated a project whereby 6 flow transmitters which are all 4-20 mA current loop are to be historically trended in Intouch. The Flow Meters are quite remote but there is already an ethernet cable ran to that vicinity. I need to convert 4-20mA into ethernet then plumb them into a switcher and im off, intouch part should be a doddle.
Was wondering if there is a known method for converting this or should something like this do the trick??:-

www.jmcanty.com/Products/Vector/TA9688-1.pdf

Many Thanks and merry xmas to all at PLC Talk!

LH
 
There are many devices to do this. As far as the Canty, you need to figure out what protocols it is capable of communicating over Ethernet
 
As TW said, many companies offer remote or field I/O devices, for example AutomationDirect.com and Allen Bradley. Note that all Ethernet devices don't talk to each other. You need to determine the protocol your Intouch is using and match it. For example Allen Bradley's TCP/IP won't talk to Modbus TCP, event though the Ethernet link is electrically compatible.
 
Hi all,
I have been allocated a project whereby 6 flow transmitters which are all 4-20 mA current loop are to be historically trended in Intouch. The Flow Meters are quite remote but there is already an ethernet cable ran to that vicinity. I need to convert 4-20mA into ethernet then plumb them into a switcher and im off, intouch part should be a doddle.
Was wondering if there is a known method for converting this or should something like this do the trick??:-

www.jmcanty.com/Products/Vector/TA9688-1.pdf

Many Thanks and merry xmas to all at PLC Talk!

LH

Heres an option for you. Try putting a small PLC in the field to bring in the 4-20ma inputs over Ethernet. You will need a CPU with Ethernet and two 4 channel analog input modules and an OPC server to talk to Intouch. I can send you a list of parts if you are interested that will work for you.
 
many thanks all for your replies, after further discussions with people onsite, looks like this mod might grow into a site wide thing incorporating our chiller plant and many other things, so i am going to go down the PLC route rather than use seperate remote i modules.

Thanks everyone for your help...appreciated!🍻
 
You might also check out Opto22, they have a whole range of I/O that uses ethernet. Their modules are small and cheap, typically 2 & 4 input so you wouldn't have to buy any mor I/O than you need.
Roy
 
Are the transmitters HART compliant? If so, there is a new wireless HART standard. Many vendors are selling retro-fit units that will transmit the HART data via wireless to a central collection point. As of now they are not recommending it for control, but you are only monitoring and historizing, might be worth checking into.
 

Similar Topics

Troubleshooting an issue in which a 1756-IF8 AI card is usually working fine reading a ~12mA current loop from a device. When firing a relay from...
Replies
6
Views
2,144
Hey Guys I have a Micrologix 1400 that has Analog output card 1762-OF4. I need the analog output card to send a signal to a receiver (I am using...
Replies
24
Views
5,744
Hello to all, I have one application where I created a simple control loop which works very well. Now, I want to increase the availability in the...
Replies
8
Views
2,821
Hi All, I don't do much analog, and I do even less with 4-20ma current loops. Here's what I'm thinking of doing; I'd like a double check so I...
Replies
14
Views
7,282
I have been told that I need a resistor across an RS232 connection for it to work. That the RS232 loop is a current loop and it is 4-20ma. Is...
Replies
11
Views
4,169
Back
Top Bottom