Hello, I was wondering if anyone got any suggestions for equipment that might be used to determine if a motor is running or not. Nothing too advanced, not undershoot or overshoot. Today the feedback from the motor that determines if it's running or not is only a NO on the contactor. If it's unplugged it will still say that it's running.
 
You are right, the NO contact on the contactor basically tells you that the control circuit is healthy and the contactor has been energised.

For many drives (albeit conveyors, rotary valves, fans) we have a rotation sensor on the driven part.
We also fit local isolators with an aux contact, so that if this is switched off, then you lose the healthy signal and cannot energise the contactor.

If you have an ammeter on the motor and know the normal loaded current, then if that is much less, then assume it is not running.
 
Our first version of sensing phase current was something like that.
But we found that the fixed leads were a hassle. Unless you PLC is right next to the power curcuit(s) you want to monitor, you have to provide some intermediary terminals to extend the wires.
 
Our first version of sensing phase current was something like that.
But we found that the fixed leads were a hassle. Unless you PLC is right next to the power curcuit(s) you want to monitor, you have to provide some intermediary terminals to extend the wires.

Difficult to know the set-up but just put it at the cabinet end on the output of the contactor :confused:
 
I've used the NK devices in various configurations for years. They have lots of models, including many with terminals instead of pigtail leads. They are also available at AutomationDirect.com
 
i don't know whether the motor got coupling or not,i only guess

may i know what type of motor do not have coupling?
 
Hello, I was wondering if anyone got any suggestions for equipment that might be used to determine if a motor is running or not. Nothing too advanced, not undershoot or overshoot. Today the feedback from the motor that determines if it's running or not is only a NO on the contactor. If it's unplugged it will still say that it's running.

We could serve you better if we had more detailed info on the load you are trying to monitor. Is it a fan, pump, conveyor, etc.?

Also I know a lot of people do it but measuring current alone is really a poor indicator of accurate load for protection purposes. Measuring power is much more accurate and linear. Motors still use current even under no load as you have magnetizing current and no load losses to deal with. Each motor no load current is very different and depends on windage, air gap, etc.

For accurate power measurement I like to use this line of products http://loadcontrols.com/

I have a couple hundred of these installed and we really like them. We use them on conveyors, slurry pumps and plastics reclaim and edge trim grinders.
 
Last edited:
We could serve you better if we had more detailed info on the load you are trying to monitor. Is it a fan, pump, conveyor, etc.?

Also I know a lot of people do it but measuring current alone is really a poor indicator of accurate load for protection purposes. Measuring power is much more accurate and linear.

For accurate power measurement I like to use this line of products http://loadcontrols.com/

I have a couple hundred of these installed and we really like them. We use them on conveyors, slurry pumps and plastics reclaim and edge trim grinders.

The motor is used in a vibration feeder. AC 230V, pulling 11A at delta.
 
It is to give feedback to intouch screen if the motor is on or not. Now it can give a false impression if the plug is out, but the contactor is activated (will show that it is running). Also it will be used in the program as a interlock function for other equipment.
 

Similar Topics

We have a customer that wants to monitor current on all the 480v motors on a piece of equipment - 5-6 motors, all 5 HP or less. Ideally, I'd like...
Replies
9
Views
3,697
Greetings from Michigan. I have an application where we want to monitor voltage and current coming off the output side of the AC motor drive. We...
Replies
12
Views
4,967
Motor control advice, I've been programming a transfer system that transfers parts from one station to the next. The FWD and REV travel is...
Replies
51
Views
28,519
Has anyone here a lead on monitoring AC current? We are rebuilding a machine that has approx. 70 heater zones, and in the past, each has been...
Replies
28
Views
11,788
I have to replace temperature controllers for an extruder and it is a retrofit. Each zone (there are 8 per controller, 72 loops in total) has up...
Replies
4
Views
3,201
Back
Top Bottom