Current monitoring/Motor load monitoring
The motor is used in a vibration feeder. AC 230V, pulling 11A at delta.
In that case, I recommend that you sense all 3 phases. With vibrating equipment, there is a high risk of wires coming loose or breaking.
We always use the aforementioned Carlo Gavazzi relay on all 3 phases on all motors on vibrating equipment. As an added bonus, it also covers all other imaginable causes for that the motor is not starting up.
I think he may have a single phase vibration feeder. If 3 phase then yes monitor all 3 indeed. if it is 3 phase I would again recommend load controls as they have a easy compact unit that handles all 3 phases and will do a switch and / or transducer output.
It's 3 phase Delta.
We have a customer that wants to monitor current on all the 480v motors on a piece of equipment - 5-6 motors, all 5 HP or less. Ideally, I'd like...
3,698
Greetings from Michigan. I have an application where we want to monitor voltage and current coming off the output side of the AC motor drive. We...
4,967
Motor control advice, I've been programming a transfer system that transfers parts from one station to the next. The FWD and REV travel is...
51
28,522
Has anyone here a lead on monitoring AC current? We are rebuilding a machine that has approx. 70 heater zones, and in the past, each has been...
28
11,789
I have to replace temperature controllers for an extruder and it is a retrofit. Each zone (there are 8 per controller, 72 loops in total) has up...
3,201