Current monitoring/Motor load monitoring

The motor is used in a vibration feeder. AC 230V, pulling 11A at delta.
In that case, I recommend that you sense all 3 phases. With vibrating equipment, there is a high risk of wires coming loose or breaking.
We always use the aforementioned Carlo Gavazzi relay on all 3 phases on all motors on vibrating equipment. As an added bonus, it also covers all other imaginable causes for that the motor is not starting up.
 
In that case, I recommend that you sense all 3 phases. With vibrating equipment, there is a high risk of wires coming loose or breaking.
We always use the aforementioned Carlo Gavazzi relay on all 3 phases on all motors on vibrating equipment. As an added bonus, it also covers all other imaginable causes for that the motor is not starting up.

I think he may have a single phase vibration feeder. If 3 phase then yes monitor all 3 indeed. if it is 3 phase I would again recommend load controls as they have a easy compact unit that handles all 3 phases and will do a switch and / or transducer output.
 
I think he may have a single phase vibration feeder. If 3 phase then yes monitor all 3 indeed. if it is 3 phase I would again recommend load controls as they have a easy compact unit that handles all 3 phases and will do a switch and / or transducer output.

It's 3 phase Delta.
 

Similar Topics

We have a customer that wants to monitor current on all the 480v motors on a piece of equipment - 5-6 motors, all 5 HP or less. Ideally, I'd like...
Replies
9
Views
3,695
Greetings from Michigan. I have an application where we want to monitor voltage and current coming off the output side of the AC motor drive. We...
Replies
12
Views
4,966
Motor control advice, I've been programming a transfer system that transfers parts from one station to the next. The FWD and REV travel is...
Replies
51
Views
28,498
Has anyone here a lead on monitoring AC current? We are rebuilding a machine that has approx. 70 heater zones, and in the past, each has been...
Replies
28
Views
11,785
I have to replace temperature controllers for an extruder and it is a retrofit. Each zone (there are 8 per controller, 72 loops in total) has up...
Replies
4
Views
3,199
Back
Top Bottom