I'm using a Danfoss drive FC302 connect via profidrive to a Siemens PLC 315.
My problem is how can I read from the drive a current upper than 327 A?
How can I setting the PCD drive for 32bit motor current?
Thanks!!!
Isn't this automatically scaled when you use a larger machine?
Also, contact Danfoss support, they are very knowledgeable
Hi David!
You should be able to read up to 675 A in one PCD channel.
If you need more you map the motor current in 2 PCD channels, as long as you keep them in Par. 9-16.2 and 9-16.3 OR 9-16.4 and 9-16.5 OR 9-16.6 and 9-16.7 OR 9-16.8 and 9-16.9 it will automatically use the 32 bit for your current instead of the 16 bit usually used.
Best regards,
Michal_dk