The problem is I have an application made in factory talk view studio Ver. 5 (CPR9), and when I download to Panelview Plus 1000 ( CPR9 firmware ) the data log don't work, when I change screen in HMI all data in trend lost.
This same application I have downloaded the PanelView Plus 1000 (CPR7, firmware old) and works well
I have enable data log in startup options
I have all tags in data model ( 7 tags )
thanks, any suggestion is great.
When you selected the pens to display, did you make sure you selected them from the data log model you created, because if you selected them from the tag data base you will get your pens operating as you have described
Hi, thanks everybody
The solution was in the database tags.
I created new tags and I enable options memory and retentive in type tags some like that:
Newtag( type: memory,retentive,initial value=0)
Oldtag( type: device,::[PVRIO]B9 34 tag adress )
So I created a macro {Newtag}={Oldtag}*1
enable all new tags in trend and datamodel
in startup options enable datalog and macros
and work fine
Hi, well I do not remember how did that because we changed the application on all HMIs, In specific what do you need fix?
what is your the version in HMI and version of FactoryTalk View Studio?
In my experience, the problem when the datalog dont work is in the firmware, I had the same problem on firmware v5.0 and v6.0, the solution was upgrade firmware in HMI v5.0 to v5.1 and v6.0 to v6.1
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
We are using RED LION HMI Since las 15 years. To day we have found that My log file has data up to 22 Mar 2024 1:16. Then After new Log File is...
23
1,477
Hi , i currently have data logs running but i need a way to link a tag to them so if there ever not running i can trigger an alarm? what is the...
1,843
Hi all, I am working on a project in Tia Portal v17, and I have a function block that is responsible for data logging. This data log begins once...
1,803
I am stuck on something, and would appreciate if someone might have a suggestion to help me. I need to automatically email CSV log data from...
1,789