Hey ya'll and Ken if you're out there,

I've encountered one of the strangest dnet issues I've ever come across. I have a Rockwell estop box, connected to a rockwell safety block, connected to a dnet network. When I hit the estop, the other 4 or so dnet cards in the chassis to fail. We're talking corrupted scan lists, etc. Recovery involves power cycled the entire bad network; others recover just fine and scan lists are fine.

Ok, so finding that the estop box has a bad contact, that makes sense. But i'm still troubled for an explanation. All the dnet issues ive ever troubleshooted were at the very least isolated to that network albeit sometimes not to the particular device causing trouble. This is the first time I've seen a device on one network shaft other networks.

Any theories? Thanks.
 

Similar Topics

Hello all, Just airing this out to see if I've missed any trouble shooting step. This is for PLC5 DeviceNet Scanner. My module is the AB...
Replies
1
Views
663
We have an application where we're communicating between a 1769-SDN a 3rd party device. For the most part things work fine. We're reading maybe...
Replies
9
Views
2,742
Hello All, I wonder if some of you can give me some insight in this problem that I have. Here are the symptoms 1. 1756-DNB/A DeviceNet Comm...
Replies
12
Views
3,587
Hi, I'm having issues commissioning a new PointI/O module (1734-4IOL) on an existing DeviceNet network (1756-DNB). I am adding the 4IOL module to...
Replies
1
Views
831
I'm having a strange issue where the operator can input a desired speed in 0-110%, and the scaling will correctly translate that in Hertz to the...
Replies
6
Views
2,290
Back
Top Bottom