Hello.

I need to create alarms wen one of the nodes on the devicenet network goes to error.

But a have not found a register on the PLC with the error codes of the devicenet network.

I am working with a PLC SLC500,

Any ideas about hot to solve this problem.

Best Regards.
 
The status data available from the 1747-SDN is contained in an "M1" module data file which should be copied from the module into an ordinary Integer file in the SLC-500 controller.

The layout of that data file is shown in the 1747-SDN User Manual, in Appendix D.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um655_-en-p.pdf

The 1747-SDN does not have as extensive a status table as the 1756-DNB, but the Active Node and Fault bit arrays should give you the basic status information.

I have written logic to capture the scrolling device status values, but have not worked on that in several years and do not have the notes to support it.
 

Similar Topics

We have a devicenet consisting of 15 PF755 drives in a centerline MCC, and on a separate trunk cable coming off the scanner, a single PF525 in a...
Replies
0
Views
352
Hello PLCs.net! I have encountered an issue where multiple PLCs over our line have not had their devicenet .dnt files saved properly. I have...
Replies
2
Views
1,607
I have running devicenet network consist of 1796-SDN and 14 powerfexes, three consits of power flux 700 and remaining consits of power flux 40 ...
Replies
12
Views
6,094
Evening All, Little bit of background - Last week I'm asked to attend a "plc fault" with one of the techs - usual story of very little info...
Replies
11
Views
4,074
I'm currently using a 1734-ADN Point I/O adapter. I would like to know how i add this to an existing Devicenet Network? I understand it is a...
Replies
2
Views
1,711
Back
Top Bottom