DH+ using non-standard bluehose

larrybray

Member
Join Date
Oct 2008
Location
Dublin
Posts
12
Hey,

Has anyone ever used any of the armored bluehose cables for a DH+ network? I have a remote building with a SLC 5/04 that has an inaccessible cable tray running to it. There is another tray carrying medium voltage cables that is accessible. I'm guessing that the standard 9463 bluehose would be susceptible to interference on this tray, but could I use high flexibility bluehose, 9463F, or an armored belden, e.g. 129463, 139463 or 189463? If I could, would the entire network need to be this cable or can I mix and match?

Cable specs @
https://edeskv2.belden.com/Products/#s=dh+&r=0

Impedance, inductance and capacitance values are the same as 9463.
Both trays are outside, is 9463 rated for outdoor use?

Thanks.
 
Ignoring the details of the various belden cables, you asked about running the communications lines with medium voltage (>1kv) power.

This would be a code violation (the Belden cables that you referenced are rated for a max. of 600VAC), and an all-around bad idea.
 
larrybray said:
ahem, my mistake. low voltage, the cables carry 400V. mixing up my terminology!

All of the Belden cables that you considered are rated for 300V. If you want to run them with 400V power cables, the communications cables must be rated for at least 400V as well. It looks like the 3072F, 3073F, 3074F cables are designed/approved for that application.
 

Similar Topics

Hi, I want to try and use a Ethernet device in my RSlogix 5000 program. As far as I know, no-one has ever used it with a PLC. The device is a...
Replies
16
Views
3,302
Hey all, First post! I am trying to embed a web browser into my application to enable us to watch live feed of our AXIS IP Camera. The problem is...
Replies
0
Views
928
I'm working with a Siemens S7-1215 PLC for the first time. I typically use isolated analog I/O in my projects, but this particular CPU comes with...
Replies
5
Views
5,077
I have a limited background on the subject so please bare with me. My experience is mostly with the mechanical aspects of the process;) We have a...
Replies
31
Views
6,925
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
Replies
0
Views
37
Back
Top Bottom