DHRIO not communicating
JoelV
Apr 2015
Jackson
We have a DHRIO module that is only using the remote I/O
to talk to (4) Hardy scale systems. Yesterday one of the
maintenance technicians turned the power off to one of the
scales and after powering back up the scale would not
communicate through the DHRIO module. The other nodes on the
network communicated fine, but the resolution was to unplug
the RIO cable from the card then re-connect. we tried powering
down the processor and toggling from run to program beforehand
but they didn't work. Has anyone ever had a similar issue.
The module didn't show any faults but after removing the plug
the scale started reading and so far no more problems.
Thanks in advance
That sounds like a situation in which the scale needed to receive a BTW for configuration prior to responding to the BTRs that receive data from the scales. Either that, or a fault on the BTR stopped the logic that should be triggering repetitive reads from the scale.
I would look at the logic for both the BTW and BTR associated with the scales. If you replicate the problem while monitoring this logic online, then you should be able to see where the problem lies.
hello, I have a problem with my AN-X2-AB-DHRIO Prosoft module, I can't connect with the module because I lost a microSD card that has firmware and...
404
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
430
I have a 1756-L81e v32 using a DHRIO v7.001 in RIO scanner Driving (7) 1771 ASB Modules @ 115k baud. The Racks RPI are set at 48msecs. This system...
916
Hey guys, We recently picked up a new customer that just finished a controls upgrade with some other systems integrator company. They upgraded to...
1,774
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,396