DHRIO Receive System Fault From SLC 5
rs14smith
Aug 2012
TN
61
I've encountered a situation where the SLC 5 connected to a Compact Logic via DHRIO does not send the Compact Logix a fault notification if the system (SLC 5) faults out. The reason being, the RIO card inside the SLC 5 rack is still communicating just fine with the DHRIO (in the compact logix rack), however, the SLC 5 has a fault in the processor (S:...bit) but I do not know how to let the compact logix know that.
Currently, I can only detect if there is a communication fault between the DHRIO and the RIO in the SLC 5.
Does anyone know of a solution?
OK this doesn't make since to me. What PLCs do you have and how are they connected? There are several SLC that can talk on RIO. I haven't seen a DHRIO card for a compactLogix. I have seen them for a ControlLogix.
How is the network setup? Is the SLC using a master or a slave card? I think the slave was a DM card.
I agree with Jeff that you are likely using a ControlLogix and a 1756-DHRIO module, with a 1747-DCM or similar module in the SLC-500 chassis. You had a recent thread with this architecture (with a MEDAR variant of the DCM).
This architecture doesn't include any mechanism for determining the runtime status of the SLC-500 controller.
You could "roll your own" very simply by using part of the Output memory as a watchdog; if it doesn't change within a certain period of time, your ControlLogix program can consider the SLC-500 program to be faulted or stopped.
I've never had to create a watch dog but have heard the name several times.
Could I use just standard bits on the SLC-500 side to create my watch dog logic, or are there special bits I need to use to properly create a watch dog for the program?
Since it is very hard to even get this rare processor fault, I want to be sure that the logic works. :)
hello, I have a problem with my AN-X2-AB-DHRIO Prosoft module, I can't connect with the module because I lost a microSD card that has firmware and...
402
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
430
I have a 1756-L81e v32 using a DHRIO v7.001 in RIO scanner Driving (7) 1771 ASB Modules @ 115k baud. The Racks RPI are set at 48msecs. This system...
914
Hey guys, We recently picked up a new customer that just finished a controls upgrade with some other systems integrator company. They upgraded to...
1,774
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,396