difference between DCS and PLC
rob63
Mar 2015
uk
69
I was just wondering why a setup would be referred to as a DCS rather than just a standard PLC system?
I was on a site the other day and it was the first time i had come across this particular phrase. The setup was a couple of 300/400 controllers in a switch room with an engineering station essentially a pc running pcs7. This was connected to a few remote i/o next to the machine.
The only difference i can see (i don't know very much though :-\ ) from a standard setup controller setup was all of the i/o was able to view on a pc rather than plugging a laptop in??
See a similar thread, and my post from it below:
http://www.plctalk.net/qanda/showthread.php?p=660813
Simatic Manager/S7 is a PLC programming package, which could be combined with a SCADA or HMI package to allow for control. You can program whatever you want, but it doesn't do much to get you pointed in the right direction.
PCS7 is a DCS (distributed control system), which includes HMI, PLC, IO, ETC. These tools are typically used in Process facilities, like chemical plants, oil refineries, etc.
PCS7 combines S7 v5.5 and WinCC SCADA, and adds a bunch of extra stuff to integrate them. It makes the code very structured, based on the idea of a Process Object, which is one motor, one valve, etc. The PO includes all the values for that objects, including setpoints, actual values, temperature, runtime, maintenance data, etc. It includes libraries with both code for common types of objects, as well as HMI faceplates that automatically link to them. It allows you to organize these process objects by the area of the plant they are in, so you can easily monitor how your plant is performing.
The difference between PLC + SCADA and DCS is more historical then practical. Now, both types of systems can do most of the same things, but 20-30 years ago the differences were much bigger. The difference now is mostly on the approach to programming, and how the customer wants to think about his solution.
Excellent explanation MK42. I read a few (old) threads about it elsewhere and it just confused me. The idea behind it is pretty obvious to me now.
hi! i am quite confused about SCADA and DCS.. is there any differences between the two systems?. thanks for the info..
2,353
What is the difference between PLC and DCS control system? According to information, PLC is an completely industrial automation system, where as...
3,112
I want to know what is the main difference between PLC and DCS.if PLC Perform every task why we use DCS.Plesae can some one tell me about DCS5000...
17
27,509
Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
1,456
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
28
4,176