Discrete DCS <--> PLC interfacing without a Gateway
Scott180zip
Oct 2008
Brunswick, OH
16
I need to control a solenoid currently connected to a PLC from an ABB DCS in a remote part of a plant. So the PLC and DCS would "share" control of the 24VDC Solenoid. Any ideas on the best way to do this without a gateway? Ex: Use a PICO controller as interposting relay, etc..?
Use an interposing relay but it can be a cheap SPDT type like an ice cube for about $15. Use the ABB to energize the relay when solenoid action is needed. Wire the contacts at the relay to an unused PLC input. Program the PLC to recognize the digital input as a call to energize the solenoid.
Thank you. Currently the solenoid is operating air to a diaphragm pump. This pump runs when the PLC calls for it. Doesn't Adding this interposing relay now opens up a conflict between the DCS and the PLC when both call for the pump at the same time?
There would be no conflict if the original call by the plc and the digital input representing the ABB-activated relay were programmed in parallel (an OR statement). That way if either the PLC or the ABB called for the solenoid, it would actuate.
Reply to Power Supply (Re:Milldrone):
If I use for the interface a dry contact relay, wouldn't the power supplies be isolated? Therefore it would not matter, correct?
Thanks...
good day friends, With regards to the Honeywell Experion analog input/output cards, my understanding is that we can de-activate every single...
1,231
Hi Everyone, Thought I had it figured out but I came to the conclusion it would not work. Here is what I'm working with... 1769-L30ER Flow Meter...
24
742
I'm building a hydraulically-operated tractor-mounted boom that will be used to read temperatures within bulk material piles. To simplify the...
715
Hi Everyone, We are EDAC Electronics Australia and we provide wireless automation solutions and I/O distribution products, with expertise in...
825
Hello, I'm in the process of converting a slicer from an Ultra3000 drive to a Kinetix 5100 using the KNX software version 4.00. The current...
554