Display Devicenet values on a PC
DaveZR2
Feb 2010
Boston
58
Hi all, hoping someone can jump start me here.
I have a plant running on Devicenet. I'd like to throw FactoryTalk View ME (or some similar application) onto an existing PC to read/write to some Devicenet values.
What's the simplest way to do this?
I'm assuming I would need:
A Devicenet scanner card for the PC (any recommendations?)
Communications software for the PC? (Does RSLinx handle this?)
HMI software for the PC (thinking FactoryTalk View ME, but open to suggestions)
Any help would be greatly appreciated.
I already have: FactoryTalk View Studio, RSNetworkx on my laptop, and a 1770-KFD to access the network
Is there a logic controller involved in the system ?
To use the old serial 1770-KFD, you would need a license for RSLinx Classic, and some substantial knowledge about the class/instance/attribute objects of the devices you want to communicate with.
To my knowledge the modern RSLinx Enterprise CIP generic driver only bridges over Ethernet to other CIP networks (ControlNet and DeviceNet) and does not have a 1770-KFD or other direct device driver.
Thanks for your response
No PLC, but there is a PC running Wonderware InControl with 4 DeviceNet cards that does all of the logic. My initial thought was to modify the InControl code to write existing values to to a new node (the new node would be the new PC with FactoryTalk ME Station on it)
To use the 1770-KFD for what? My only intention was to use that to troubleshoot the DeviceNet network from my laptop if necessary, not to use it with the new PC. I was hoping that the new PC would only communicate with the InControl PC over DeviceNet. Does that make sense?
I'm not sure what you mean by this. My intention was to add a DeviceNet card to the PC to make it a node on one of the existing DeviceNet networks, not to use the 1770-KFD.
I may be totally off. With my existing setup, as I described it, is there an easier way to display some values on a remote operator interface or PC?
DeviceNet is a low-level, serial bus based protocol intended to allow a system controller(PLC) connect to remotely located I/O and instrumentation.
The 'DeviceNet data' consists of PLC Reads/Writes from/to field located I/O and instrumentation.
My point is, as Ken also inquired about, that HMI data always originates from or ends up within a PLC; HMIs(Terminals) and HMI applications(SCADA) read from and write to PLCs.
Your DeviceNet network is connected to a PLC; the data you are intending to display is located on said PLC.
Locate the system controller, acquire its logic application, locate the DNet originating data and 'extract' it via HMI application (terminal or PC based)- that's it...:D
You will most likely need the software the PLC application was created with (and the currently running application file) in order to point the HMI application to the memory locations which contain the DNet data. We do not know about the controller type hence the CPU software requirements.
As for the PC running FTV ME application, depending of the intended complexity (how many displays you will need to use), acquire the corresponding FactoryTalk View ME Station licenses listed within https://www.rockwellautomation.com/...factorytalk-view-me.page#ordering-information.
The HMI application will be created using the FactoryTalk View Studio and ran using a PC containing the FTV ME Station purchased license.
Are you planning to monitor the I/O data going to and from the InControl controller to the slave devices, or do you want to read parameters from programmable devices, independently of the controller ?
A computer equipped with a 1784-U2DN (USB) or a 1788-EN2DN (networked) bridge device might be suitable for giving an HMI computer access to parameters in programmable devices.
This isn't the normal use of an HMI connected to a low-level fieldbus, but it's possible to do.
Yes, I understand all of that an have all of those items already. Maybe I didn't make that clear, I apologize. My question was more about the communication driver and physical connection between the PC and the DeviceNet network.
Planning to monitor/modify the I/O data going to and from the InControl controller to the slave devices. Similar to an old DeviceNet PanelView Standard but substitute a PC running something similar to FactoryTalk ME Station. My real questions are: is FactoryTalk ME Station the way to go or is there a more appropriate application (not looking to break the bank)? Should I use a DeviceNet PC card or is there some other gateway? What is there an RSLinx driver that will work? Are there any DeviceNet HMIs that I might consider using instead?
Thank you!
Is there anyway to make the display of the devicenet scanner code translate to the factorytalk software to the HMI? 🙃
2,882
Hi everyone, I'm looking for a "digital panel meter" type display that is capable of displaying a value from a CompactLogix PLC over EtherNet/IP...
7,187
Hello, I'm using FactoryTalk View ME V10. I created a valve as a global object with multiple parameters and when the object is being used at the...
135
Hello all, I was modifying an HMI in factory talk and went to change a go to display button using the ... to select from a list as I had done...
182
Is there a way to add a local message display to Studio 5000 View Designer? If its there, I’m not finding it. I have used them in older versions...
417