Dosing equation
Snap25
Dec 2014
Michigan
237
Do anyone know the equation in picture below?
I set up a dosing system to calculate a new batch but I can't seem to figure out the computation to dose a certain concentration into the existing concentration to reach a concentration set point !
I started converting everything to wt% to vol% then it got late and I'm getting more confused!
Info you may need to help me get there.
Bulk solution is 50% NaOH which is 12.7 pounds per gallon
Water is 8.3
For sake of example let's assume these parameters
Tank targets : 11% NaOH concentration and volume @ 2200 gallons
Current Tank status : 8% NaOH concentration and volume @ 1885
So I'm down 3% on my NaOH and need 315 gallons.
I would like to figure out a formula to know at what concentration mixture the 315 addition should be to reach 11%.
I was getting really close to figuring it out but last track of what I was doing while shuffling through a dozen examples on my notepad.
2dDXo
This is how I would work it out.
NaOH SP in gallons is: 242 Gals
NaOH PV in gallons is: 150.8 Gals
You need to add: 91.2 Gals
Water deficit is: Capacity - Actual : 2200 - 1885 : 315 Gals
(NaOH Required / Water Required ) * 200
* 100 for % of NaOH if at 100% concentration, as yours is 50% times by 200
So in this example you need to add 315 Gals of a 57.9% concentration of NaOH / Water.
Hi all, Have a job where we're using peristaltic pumps to dose CL2 for wastewater, pretty standard 4-20mA flow pacing signal being used, no PID...
1,712
Is it good idea to use ultrasonic clamp type of flowmeter for water dosing? I already using the flowmeter pulse output by setting to 10L per...
1,300
Can anyone help me with this project(chemical dosing pump) using logo siemens software: When you press the start push button, it should actuate a...
59
6,538
Hey everyone, I was on a customer's site on friday where they have a large bioreactor that they bought secondhand from a previous user. System is...
22
4,502
Hello, I want to ask about two instruments, the dosing pump and the rotary valve. I will be using the dosing pump to dose a liquid, and the...
2,926