Double Automatic Door....please help
Nov 2015
Korea
So I'm on a beginner class(infant level), trying to build a 'double automatic door'
and i'm having a lot of troubles..
getting a lot of errors
theses are the requirements.
sorry.. this is the best i can draw
(Explanations for the pic)
-Sensor S1 is in front of a door1, S2 is between two doors and S3 is behind the door2
-M1 is Door1's opening motor and M2 is the closing one
-limit switch L1 turns ON when Door1 is fully opened and L2 turns ON when fully closed
-M3 is Door2's opening motor and M4 is the closing one
-limit switch L3 turns ON when Door2 is fully opened and L4 turns ON when fully closed
(Requirements)
1.When Sensor S1 or S2 senses someone, Door1 must be opened for 3seconds.
2.When S1 or S2 is OFF, Door1 is closed.
3.When Sensor S2 or S3 senses someone, Door2 must be opened for 3seconds
4.When S2 or S3 is OFF, Door2 is closed.
well this is how much I managed to do
if there's something missing or wrong, could you please tell me.
i guess I can't study this field with only a book..;
Start by only looking at only one door.
Door 1:
OPEN DOOR:
S1 or S2
CLOSE DOOR:
3 sec Timer and not S1 and not S2
In the first rung put S2 in parallel with S. This would then allow the door to open if either S1 or S2 are present. (M1)
M2 Closes the door.
Use the timer and not S1 and not S2 to start the door closing.
Once you are happy with the operation of the first door, apply the same logic to the second door.
Hope this helps you out.
Try1 door at a time first
Try to get one door to work first. You are trying to much first.
A few things wrong
1. on rung 2 you have limit 1 opening door 2 no relation as per discription.
2. you are only using 1 sensor and 1 timer in your program.
Do not give up but I do recomend a cheap PLC to play with.
Automationdirecthas somelowpricePLC thtuse free software.
Good luck
Door 1:
OPEN DOOR:
S1 or S2
CLOSE DOOR:
M2 Closes the door.
You're right. should've done this one by one.
would this be fine for the first door?
It looks correct. The best way is to simulate the program. As 'just the cowboy' suggested, I would try this out on a PLC. You could also try this out on a simulation package.
http://support.automationdirect.com/products/domore.html
The above link is for the Do-More Designer Software from Automation Direct. It is a full PLC programming package for the Do-More PLCs plus a Simulation. It is also free of charge.
Regards,
Regards,
wow. thank you. really helped me through
What is the simples way to do a double click of a button in a ladder logic. New here and I hope this has not been asked before.
22
539
Hi All, I'm keep getting double quotes in between selections rather than the beginning and the end. Here's the script and please help to find...
802
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
538
Hello All, IÂ’m starting a new project where the plc is connected throught LAN with external software which write some data on PLC db, obviously...
520
Hello. I have been working on my first plc project for a while now. I just ordered all the parts that I need and before I did that, I created the...
2,050