Drive Question

arocon

Member
Join Date
Oct 2006
Location
Dubai
Posts
171
Could anyone please tell me how derive torque limit value ? Is it from motor specification or process specification
or drive specification ?
 
I always have to get the book for that specific drive do a little reading and you should easily figure out what you need. generally torque values come from the motor. That is asuming that you have the process requirements and just need to program your drive
this is From http://www.elec-toolbox.com
To calculate motor full-load torque, apply this formula:
T = HP x 5252
rpm
T = torque (in lb-ft)
HP = horsepower
5252 = constant
rpm = revolutions per minute

Example: What is the FLT (Full-load torque) of a 30HP motor operating at 1725 rpm?
T = HP x 5252
rpm

T = 30 x 5252
1725

T = 157,560
1725

T = 91.34 lb-ft


 
Last edited:

Similar Topics

I have a few questions about Studio5000. 1. Why is my RA folder so big? its well over 100 GB. 2. How do you delete versions or extra files...
Replies
3
Views
279
Hello all. I am hoping someone here has installed a Danfoss VLT Midi FC 280 and connected an encoder to it. I am just trying to make sure I select...
Replies
0
Views
464
A curious thing: If a Indradrive servo drive has firmware 20.xx in it, it can communicate with the ControlLogix using a generic (implicit)...
Replies
3
Views
1,701
Hi, I have little experience with inverter drives and was planning on using an ABB ACS310 drive to power a linear positioning system. But i had...
Replies
8
Views
2,287
Members of this forum helped me out a great deal a couple of years ago with a question I had regarding acceleration during torque control of...
Replies
8
Views
4,406
Back
Top Bottom