driving a freq var by a plc
juan
Apr 2003
50
I was wondering if its possible to send certain code from the plc program to the frequency variator in variable words, in that way I use one code to drive the motor(by the freq. var)in the left direction and another code for right position. By code I mean the values in the variable words. If this is possible are there standard values? i'm using the Siemens micromaster.
Probably yes, but you hae to have a VFD (Variable Frequency Drive) or other device and a PLC that both have the same communications protocol and serial configuration. For example, if the VFD or control device has a serial port with Profibus cpability and the PLC has a Profibus port, the PLC can send and recieve commands and data from the VFD. You need to configure the port address and communications parameters in both devices, and you need a list of the memoryt locations in the VFD from the manufacturer that identifies the locations in the VFD memory of the data you are interested in.
Which values
There is already a connection, but I don't know which values to drive the both directions. The serial port is already established and in use.
Juan,
Just buy the Siemens "Toolbox" option. This option integrates into MicroWin. It will give you the function blocks for the USS protocol.
It is very easy to use.
toolbox??
Is this toolbox a extra hardware device of is it a software toolbox? Is this expensive an which possibilities are there available? Is this the only possibility?
102193a
Is the drive already running and you just need the control word
values for reverse? or is this a new application and you are
trying to run a micromaster drive?
already running
There is already one direction running and we want to establish to other one. At the moment we can go to the other side but ...
In the attached file the 'V' is the direction at work but the 'k' has to be improved
sorry
This file is quiet big, but the most important things about this topic are in INT0(V,K), INT3,5(resp V,K), SUBR3
Thanks a lot!
Here's a sample of USS using the toolbox.
Basically bit 14 (start with 0 through 15) of the control word needs to be ON
So-
047F-Run Forward
047E- Drive Stop
147F- Run Reverse
147E- Drive Stop
drive stop
This is the way how we can stop at any moment, but if we want to stop when the current value equals to the preset value is it the same way to stop?
Sorry I keep on asking, but it interests me a lot
Thanks Juan
We have a handful of nearly identical flywheel-driven machines. About a year ago, we installed a 15HP Powerflex 525 drive in simple V/Hz mode...
886
Is there any issue with running a VFD-controlled 3-phase induction motor in torque control mode in the braking region continuously (back-driven by...
4,038
Hello everyone, we're trying to get some information from our screwdrivers. - The control chain is IqR plc with RD77MS16, connected to MR-J4 and...
838
Hi All, trying to restore a runtime application that i have been reliably informed was created in version 10 ftview, i get the below error:-...
988
This is the tab order I have in the e-sign component in Rockwell. Is it set in stone can this be modified? The ideal set up would be to get to...
1,288