Driving a SSR with a PID Loop ???
brettshelley
Dec 2007
Durban
45
Hi guys, I am having sleepless nights over this problem!
I am reading a temperature value and using a PID routine to make sure that the temperature stays at the process value. My problem is this:
The PID loop gives me a variable from 0 - 4000 depending on where the temperature is.
How can i manipulate this so that as the variable changes, the pulse of the output is driven directly proportional to the value???
Eg, 4000 = ON
2000 = pulse 50% ie. 10ms
etc
Cheers,
Brett
PID_Output_Value/PID_Max_Output_Value * Time_Period.
Thus, if your PID output is 25% and the time period is 5 seconds, then 1000/4000 * 5 = 1.25 seconds. Your SSR is on for 1.25 seconds and off for 3.75 seconds.
In your example above you stipulated a value of 10mS for 50%, meaning you have an overall time proportioned output time of 20 mS. This is realistically way too short of a time period as your PLC scan time will be a signifcant percentage of the time proportioning period. And thats not even accounting for your IO response time and the .016 second response time of your SSR.
Thanks Alaric, that has racked my brains into gear!!!
I will ammend the programme and try it now!
Will let you know if it works!
There is a simpler way IFF the PID is in a interrupt routine.
If the PID is called at fixed intervals then one can just use the following code to turn the SSR on and off.
Code:
CO_SUM = CO_SUM + CO_NEW
IF CO_SUM >= CO_MAX THEN
  CO_SUM = CO_SUM - CO_MAX
  SSR = ON
ELSE
  SSR = OFF
ENDIF
This works well if the update time to the PID is too fast for a timer.
Hi guys, I am having sleepless nights over this problem! I am reading a temperature value and using a PID routine to make sure that the...
3,824
We have a handful of nearly identical flywheel-driven machines. About a year ago, we installed a 15HP Powerflex 525 drive in simple V/Hz mode...
890
Is there any issue with running a VFD-controlled 3-phase induction motor in torque control mode in the braking region continuously (back-driven by...
4,080
Hello everyone, we're trying to get some information from our screwdrivers. - The control chain is IqR plc with RD77MS16, connected to MR-J4 and...
840
Hi All, trying to restore a runtime application that i have been reliably informed was created in version 10 ftview, i get the below error:-...
997