The only time I have seen an EEPROM fault that was a repeat offender was in a panel where there were lots of VFD leads too close to the control wiring. We fixed it by going to shielded motor cables.
It has been many years ago, so I don't remember whether we replaced the drive or were able to clear the fault. Most likely we did both because the problem happened several times in one particular panel before we spent the money for shielded motor cable.