Hi all, yesterday I was at a customer site doing a PM and after making a couple of minor mods to the program, I went to back it up to EEPROM (yes there is a memory module installed on this 5/04 CPU and yes I was in PROG mode). Window comes up "write to EEPROM failed" and I immediately lost connectivity through RSLinx. This happened twice so I just gave up, but I have a weird feeling it actually did successfully transfer. Anyone run into this?
I think there is a write protect jumper on the EEPROM . . .
But I don't know if it has to be present, or removed . . .
Poet.
There's a bug in some older versions of RSLinx (I remember it with 2.41) that fails to properly process the "write to EEPROM command accepted" reply from the controller.
Instead of showing you the "EEPROM write command started, you will now lose connection while the controller reboots", RSLinx assumes that there was no reply from the SLC when the Write to EEPROM command was given.
This was most common with indirect connections to the controller, like DH+ via a DHRIO to a 5/04, or Ethernet via a Net-ENI.
The only way to verify that the Write worked was to Restore from EEPROM and look for the changes you made.
Hello. I am trying to change the indexes when I Paste from SLC Library and I must be doing something wrong. I tried it with a very simple rung to...
1,432
I have a few projects I want to Save As file type SLC to be able to use the Translation tool in Studio 5000 (migrating from SLC 5/03 to...
2,504
Hi all, Sorry to make my first post a request, but I was given this .RSS file and need to convert it to .SLC - would some helpful person with...
4,522
Hello. I am learning Allen-Bradley PLC programming using the RSLogix 500 emulator. So I need some help pls. I am using the RSLogix Microstarter...
4,263
Hello guys, Hopefully a simple one for you but I can't seem to find the answer listed in Rockwell's literature...
2,727