RSLogix Emulator error. "Node is not SLC-500 or PLC-5 processor"
davecole73
Jun 2013
Lagos
Hello.
I am learning Allen-Bradley PLC programming using the RSLogix 500 emulator. So I need some help pls.
I am using the RSLogix Microstarter Lite. I have properly configured RSLinx and Emulator 500. Station no. set at 0. But when I try to go online or upload, I get the error msg "The target node is not a SLC-500 or PLC-5 processor". Pls what could be wrong?
The ladder logic is saved as a .rss and it runs in the emulator.
The problem is that RSLogix microstarter does not see the emulator as a SLC-500 or PLC-5 processor. Thus, it can not read the emulator (processor) status or error.
If this can work, then I will try to clear the error I am having on a real Micrologix 1200 PLC.
emulator not seen by microstarter lite.
Microstarter Lite also cannot upload or download to/from the emulator cause of this error msg.
Verify "select processor type", driver and node. What communication drivers are you using in Rslinx?
I am not sure if microstarter lite have an option to program micrologix 1200.
About microstarter lite and micrologix 1200 compatibility, I'll look it up.
The driver used is PLC-5 EMU in rslinx.
Pls where do I go to select processor type?
And thanks a lot for your response thus far.
RSLogix Microstarter Lite (free version) does not support the ML1200, only the ML1000 and ML1100.
You should use the SLC500 Emulator driver for a .RSS file.
You change the controller type under Controller properties in your RSLogix project tree.
Hi guys, I am a total newby in PLCs, and I am currently doing a project in RSLogix 5000, using RSEmulate to Emulate the PLC, details below...
15,881
Hello i have Rslogix 5000 installed on win 10 and VM win 7 installed on this laptop. The Emulator installed on the VM7. Rslinx on win 10 does not...
514
Good Evening Gentlemen, we have a FT View SE client running in windows 7 system, now I want to update that system with windows 10. I did the...
2,722
Hi, can someone help me how to setup communication between rslogix5000 emulator and Ftview Me. Based on manual rslinx enterprise is required in...
2,127
Hi All, I am working on a project which uses compactlogix PLC and Citect SCADA. I don't have physical PLC at the moment. Need to test tag...
5,594