If there's voltage and measured impedance...
For motors, it really depends on with WHAT the "measured impedance" was measured. Matt stated that it was measured with a Fluke meter, which can only put out about 9 volts as it measures the resistance (unless it is a Fluke Process Meter which can go up to 24 volts).They have not tried an analogue meter - just a Fluke digital one -
These levels are not nearly enough potential to determine if 400 volt motor windings have a thin spot on the insulation (9 volts is only about 1.7% of the 537 peak volts for a 380-volt alternating current). In other words the operating peak voltage is 60 times more than the voltage being used to measure the windings. Voltage potential is like water pressure in a water line - at 2 PSI there may be no leaks at all - impedance looks normal, but at 60 times that pressure or 120 PSI, there could be water spraying from several pinholes - impedance is shorted to ground.
Motor windings are often not "all bad" or "all good". The windings are insulated with varnish, and it does not all deteriorate at the same time. Hot spots can cause it to crumble away at some points, and often a motor will check good (with a 9-volt ohmmeter) under low humidity, but once things get wet again, it will check bad. The ultimate test is what happens when you put normal voltage on it. The best test (short of applying line voltage that DickDV recommended) is using a Megohm meter.
Last edited: