embarrassing question regarding PID tuning
ganutenator
May 2002
kansas
1,440
I haven't had to tune a PID loop in a very long time.
It's actually a PI loop for a pulse width modulation s.v.
What was the name of that tuning method?
Zieglar or something w/ the quarter response curve blah blah blah or something?
Am I supposed to graph the error.
Sorry, I forgot. I'm old.
I think that I may be able to do it right on the plc output card as it is solid state, the amps are correct, and the process engineer is stating that he needs something like a 2 to 4 Hz.
And the card states a maximum of 1kHz switching frequency.
Obviously, there are still a lot of questions, and this project is in infant stage.
I've programmed a lot of PID loops in the oil fields back in the 2000's but I suck at tuning loops. I had starting numbers to plug in at that time.
This is different, as it will be my first PWM control.
You can graph whatever you find easiest to graph, but Z-N method has some graphical elements to the calculation (which you can do analytically) that relies on you graphing your setpoint and process variable with respect to time.
If you are trying to tune a highly aggressive loop, you could consider Cohen-Coon:
https://blog.opticontrols.com/archives/383
If you cannot overshoot, you can use IMC. I've never used it though, so I can't comment on it. In my relatively limited experience, Z-N and C-C get you a good starting point.
https://blog.opticontrols.com/archives/260
thank you very much JLand.
So, If I graph the pv and the sp and the error, should I look at the quarter amplitude dampening on the error?
p.s. I love Wisconsin.
Everyone is so friendly there.
I once was on a job and went to the gas station.
I slapped my credit card on the counter after I filled up my rental car w/ gas.
The lady said: "We don't take credit cards"
I said: "Oh no, where is the nearest ATM?"
she said: "A T what?"
then: "Just come back when you have the money"
Even the TSA were polite.
You can look at the quarter amplitude dampening on the error, yes.
Because error is just PV-SP, you really don't need to graph your error, you just look at how the PV oscillates around the SP. It gets you the same thing as graphing the error, just with the x-axis shifted from zero to the SP.
It's really up to you on how you find it easiest to visualize a PID loop. Looking for QAD on the error about y=0 or QAD on the PV about y=SP, it doesn't matter.
That said, you need to use your engineering judgement to decide if QAD is even desirable. If the setpoint is close to the limits of the machine, or if you desire rock steady values at the expense of response time, QAD is inappropriate to target. QAD is just a solid heuristic to target with Z-N and C-C tuning methods for when you want to hit your SP quick.
I actually paid the same day. But I appreciate analytical brained people w/ a good sense of humor. Yes, gas prices are insane.
All info on Z-N should be scrubbed from all sources. I would look at the www.controlguru.com site for how to tune systems.
The control guru pushes IMC tuning with is essentially pole cancelation.
I think pole placement is better but more complicated. Ron Beaufort once called that lambda tuning. Same thing.
In the end, it is worth putting in the extra effort to tune a system/plant right because the payoff is forever as opposed a few extra hours of work
BTW, you don't tune a PID. You tune a system/plant.
You haven't told us what kind of system/plant you are tuning. Shame, you should know better.
I am retired but not retarded. Age is no excuse.
Petrol station at the end of my street is currently showing £1.90 per litre, which is $8.82 for a US gallon. This time last year it was around £1.30.
On topic question, which PLC is it? I've got very lazy with using auto-tune, which isn't always perfect but it always gets the settings into the right ballpark and I can adjust from there.
It is a wago 750-862.
The process:
We are currently monitoring flow rate of a chemical that is being introduced into the water for a car wash application.
Customer wants to be able to set the flow rate from his office chair instead of driving to the car wash.
Customer knows that he can buy a device to do this, but wants to do this on the cheap.
So we think that we can buy a solenoid valve that accepts pulse width modulation to control the flow and do this with the output card of the wago (750-1500).
We are still awaiting info from the valve manufacturer.
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
169
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
71
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
93
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
92
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
82
