Emerson FX 455 drifting problem
dgilmore
Feb 2013
Florida
We have a cut-to-length line that utilizes an Emerson FX 455 drive to drive the feed rolls. The problem is that it continually creeps at a rate of almost 3 inches per minute. There is no menu item that I can change, that has any effect. I have even restored the default gain parameters with no success.
Anyone ever had this problem?
Do you have an Input assigned as Stop Motion?
And if so does it creep when stopped?
I worked on a lot of these years ago and never saw this
Have you reached out to tech support?
It creeps as long as power is applied.
We inherited this line from a sister company that we shut down in Mexico and I do not have the original copy of the RSLogix 500 program that runs the machine; which means I don't have the rung comment file, so I do not know if there is a Stop Motion bit. I have simulated a 500 part run and everything functioned, but if the line is paused, or stopped, the feed rolls creep. A funny thing is that we discovered the resolver was bad on the motor when we were installing the line and even with the motor leads removed, the drive indicated that it was creeping...with no motor and no resolver.
I uploaded the parameters and loaded them into another FX 455 we bought and it does the same thing. I am assuming that it is a programming issue since this is the first one I ever had to deal with.
Since you have the PCX software you can see what functions are assigned to the inputs
The file has 2 extensions .pcx and .lst
the .lst file can be opened in any text editor if you can post a copy of the file
Emerson Electronic Motion Controls
Subsid.:Emerson Electric Co.
1365 Park Road
Chanhassen, Minnesota 55317
(612)474-1116 Sales (612)474-8833 Service(24 hr)
BBS: (612)474-8835 FAX: (612)474-8711
Positioning Drive Information
Drive/Firmware ID: FX-455 401159-01 B4
Firmware Description: STD F FIRMWARE 26-FEB-1997
PCX Version: 7.0b
File Name: DSI_FEED2.LST
System: FX-455 Drive Only
Date: 02/13/18
Time: 15:25:45
______________________
| JOG INFORMATION |
|_________________________|
Serial Velocity ----------------------- 40.00 FPM
Fast Velocity ------------------------- 40.00 FPM
Slow Velocity ------------------------- 0.98 FPM
* Accel Time ----------------------- 2.000 seconds
* Decel Time ----------------------- 0.500 seconds
Lock ---------------------------------- Off
__________________________
| HOME INFORMATION |
|__________________________|
Home #0
Number -------------------------------- 0
Type ---------------------------------- Feed On/Offset
Feed On Velocity ---------------------- 0.00 FPM
* Accel Time ----------------------- 1.000 seconds
* Decel Time ----------------------- 1.000 seconds
Offset Velocity ----------------------- 0.00 FPM
Resolver Offset ----------------------- 0.0000 IN
Reference Position -------------------- 0.0000 IN
Home Limit Distance ------------------- 0.0000 IN
Home #1
Number -------------------------------- 1
Type ---------------------------------- Offset
Offset Velocity ----------------------- 0.49 FPM
___________________________
| INDEX INFORMATION |
|___________________________|
Index #0
Type ---------------------------------- Incremental
Distance ------------------------------ 15.0800 IN
Velocity ------------------------------ 98.00 FPM
* Accel Time ----------------------- 0.250 seconds
* Decel Time ----------------------- 0.600 seconds
Dwell Time ---------------------------- 0.000 seconds
Count --------------------------------- 1
Index #10
Number -------------------------------- 10
Distance ------------------------------ 12.0000 IN
Velocity ------------------------------ 40.00 FPM
* Accel Time ----------------------- 0.500 seconds
_____________________________
| PROGRAM INFORMATION |
|_____________________________|
Program Number: 0
Program Count: 1
Step Code Function Description Data
0 I Call Index 0
1 O Set PGO Pattern(11..11) 1
2 D Dwell Time 0.500 seconds
3 O Set PGO Pattern(11..11) 0
4 E End Program
| SUSPEND INFORMATION |
Run Program On Suspend ---------------- No
Automatic Return Upon Resume ---------- No
Automatic Resume ---------------------- No
Return/Remember Position Index Number - 0
Automatically Suspend Upon Fault ------ No
______________________________________
| DRIVE PARAMETERS INFORMATION |
|______________________________________|
Actuator Polarity --------------------- +
Distance User Units ------------------- IN
* User Distance Per Motor Revolution 0.4174 IN
Velocity User Units ------------------- FPM
* Velocity Scaling(3000 RPM Equals)- 98.18 FPM
Accel/Decel Shape --------------------- Linear
Analog Override ----------------------- No
==> Time Base Override ------------- Analog
| LIMITS INFORMATION |
Maximum Allowable Velocity ------------ 98.18 FPM
* Minimum Accel Time --------------- 0.015 seconds
* Minimum Decel Time --------------- 0.015 seconds
Maximum Torque Output ----------------- 200 %
Distance Limit + ---------------------- 214748.3647 IN
Distance Limit - ---------------------- -214748.3648 IN
Travel Limit Position + --------------- 0.0000 IN
Travel Limit Position - --------------- 0.0000 IN
Travel Limits & Fault Decel Time ------ 0.075 seconds
Stop/Hold Decel Time ------------------ 0.250 seconds
Absolute Rotary Position Limits ------- 0.0000 IN
Maximum Following Error --------------- 0.1000 IN
Enable In-Position Window ------------- No
| INPUTS INFORMATION |
Input Function Line # Polarity Filtering
0-Index Initiate --------- 0 -
1-Home(0) Initiate ------- 0 -
2-Clear To Initiate ------ 0 -
3-Hold ------------------- 0 -
4-Jog -------------------- 0 -
5-Jog + ------------------ 1 - 0.000
6-Jog - ------------------ 2 - 0.000
7-Jog Direction ---------- 0 -
8-Jog Slow --------------- 0 -
9-Travel Limit + --------- 0 -
10-Travel Limit - --------- 0 -
11-Stop Motion ------------ 5 - 0.000
12-Inhibit Drive ---------- 0 -
13-Brake Override --------- 0 -
14-Index Select ----------- 0 -
15-Home Sensor(0) --------- 0 -
16-Feed Sensor(0) --------- 0 -
17-Clear End Of Index ----- 0 -
18-Clear End Of Home ------ 0 -
19-Clear End Of Index Count 0 -
20-Clear Sensor Limit Hit - 0 -
21-Reset Fault ------------ 4 - 0.000
22-Zero Position ---------- 0 -
23-Zero Display ----------- 0 -
24-Remember Position ------ 0 -
25-Return To Position ----- 0 -
26-Clear End Of Sequence -- 0 -
27-Clear Program Outputs -- 0 -
28-Wait/Jump Inputs ------- 0 -
29-Program Initiate ------- 3 - 0.000
30-Program Select --------- 0 -
31-Suspend Program -------- 0 -
32-Resume Program --------- 0 -
33-Abort Suspend ---------- 0 -
34-Clear End Of Program --- 0 -
35-Clear End Program Count 0 -
36-Clear All Prog Outputs - 0 -
37-Feed Sensor(1) --------- 0 -
39-Home(1) Initiate ------- 0 -
40-Home Sensor(1) --------- 0 -
41-Index Direction -------- 0 -
42-Torque Jog ------------- 0 -
43-Time Base Override ----- 0 -
44-Clear Torque Lmt Output- 0 -
50-Clear Pos.Window Timeout 0 -
| OUTPUTS INFORMATION |
Output Function Line #
0-Ready ------------------ 9
1-External Mode ---------- 0
2-In Motion -------------- 10
3-End Of Index ----------- 0
4-End Of Home(0) --------- 0
5-End Of Index Count ----- 0
6-Hardware Fault --------- 12
7-Travel Limit Fault ----- 12
8-Position Error Fault --- 12
9-Home Completed --------- 0
10-Sensor Limit Hit ------- 0
11-End Of Sequence -------- 0
12-Programmable Outputs --- 11
13-End Of Program --------- 0
14-End Of Program Count --- 0
15-In Suspend ------------- 0
16-End Of Home(1) --------- 0
19-External Brake Output -- 0
20-Torque Limit Hit ------- 0
31-Position Window Timeout 0
| SELECT LINES INFORMATION |
Index Select Lines -------------------- 0
Program Select Lines ------------------ 0
External Input Select Lines ----------- 0
Programmable Output Lines ------------- 1
Programmable Output Reset Lines ------- 0
________________________________________________
| MISCELLANEOUS DRIVE VALUES INFORMATION |
|________________________________________________|
AG=1 AS=0 AV=3000
BD=0 CF1=1EF CF2=1EF
CF3=1EF CF4=1EF CN1=1FF
CN2=1FF CN3=1FF CN4=1FF
DB=0 DG=20 EG=100
EM1=4 EM2=0 FJ=0
GS0=20 GS1=0 IG=0
IN=0 JE=2 MV=3000
NV=800 NT=800 PR=0
RL0=100 RL1=0 RP=0
SF=0 SM=0 TB0=0
TB1=0 TQ0=100 TQ1=0
WP0=0 WR=0 WT=0 WP1=2000
TR=1 UN0=0 UN1=0
UN2=0 UN3=0 VG=65
XC=80 XP=0
what letter/number is on the LED display when this occurs?
inputs #1&2 are set to Jog and has no debounce time possible there is noise on this input ?? try temporarily removing the wires?
Input 5 is Stop Motion
Saw this once many years ago! Ended up making the stop signal constant as the momentary wasn't "holding" it.
Does it ever stop? Does it continue to creep for an hour, day??
I can go into the diagnostic screen and inhibit the bridge and the motor will stop. however, the velocity still indicates .25 FPM.
"A" is displayed.
When the resolver and motor leads are disconnected, the diagnostics still indicate that the drive has .25 FPM of velocity.
This has happened on the original and our spare drives.
Hallelujah!
The drive case was marked for the 3rd "on" and the fourth "off". I turned the 3rd "off" and it immediately stopped.
I will do some dry runs now to see if it holds up.
Thank you for your help!
Hi there, new to the forum, I'm excited to have found this as a place where I can learn and help when I can. Not a great number of forums like...
841
Two questions for GE/Emerson e.g. PACSystemsRX3i (CPE330): 1. Is it possible to use 2D arrays inside a function as a local member? (I can only...
51
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
112
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
108
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
980