Hello everybody

I would like to know if it is possible to simulate an exchange of messages (MSG) between two MICROLOGIX 1500 in the EMULATE 500. I performed some tests but I was not able to, maybe it is because the communication is RS-232 or the emulate is not able to simulate the necessary resources. Finally, I would like to thank everyone for their attention and patience.
 
Welcome to the PLCTalk forum community !

Emulate 500 can use a Windows COM port to emulate DF1 protocol or ASCII communications when you are emulating an SLC-500 or MicroLogix controller, including a MicroLogix 1500.

It cannot emulate DH-485 protocol.

The first thing to be certain about is that you don't have a conflict between RSLinx Classic using the same COM port as Emulate 500.

The computer's RS-232 port will have the same pinout as a DB9 port on an SLC-500 or MicroLogix 1500.

If you are communicating between two Emulated MicroLogix controllers, you can probably use a virtual COM port pair, like using Com0Com shareware, but I don't have any direct experience with that.
 

Similar Topics

Been a long time since using AB. Looking to emulate a Micrologix 1400 job before the hardware is available. Is there still an emulator available...
Replies
3
Views
1,963
Hi! I'm using RSLinx Classic, RSLogix Micro English and RSLogix Emulate 500 to emulate a Micrologix 1100 Series B. I'm able to run, program and...
Replies
5
Views
2,006
HI, is it possible to emulate a modbus program (RTU) with Allen bradley Rslogix Emulate 500? I tried, as master and slave, with a serial cable...
Replies
1
Views
1,139
I have a virtual machine on Win 10. I have Emulate v32 working with several controllers of different versions running successfully, as well as an...
Replies
2
Views
8,590
I am using Wonderware Indusoft with RSlogix Emulate 500 on my laptop. When I run Indusfot, my data are not population on HMI screen, and I get...
Replies
0
Views
972
Back
Top Bottom