I want to connect optical encoder to 1746-HSCE encoder module with distance to SLC chassis about 50 meters.
Could we get the problem with that distance?
Thank you
Charly
There is nothing inherently wrong with going this far. You just need to be more careful the farther you go.
Noise is one issue. Make sure you use shielded cable and correctly ground the shield drain. The farther you go the lower the maximum frequency you can effectively transmit. If your encoder speed is slow it's no big deal. Higher frequencies are harder to run long distances. Your encoder output driver also has an effect. If the drivers is a TTL level driver (5 VDC) your combination of speed and distance will be less than with an HTL driver (24 VDC).
Your encoder specs should be able to tell you how far and at what frequency you can transmit. The fact that you are connecting to a 1746-HSC as opposed to another device doesn't matter as much.
Keith
HSCE Encoder Cable
For a 8-24vdc powered encoder with a 5v DLD output you can run a Belden 9330 type 22 AWG cable (4 twisted/shielded pairs) the maximum 1000 feet that the 1746-HSCE specifies.
Keith
In fact, just the opposite is true. All cables have capacitance. This capacitance must be discharged and recharged each time the encoder output switches. It takes longer to discharge and charge a capacitor to 24 volts than to 5 volts. Check out encoder specs for the max. cable length at a given frequency and you will see a 5 volt signal can go further than a 24 volt signal.
Good afternoon! Please help, the following situation happened: Connected encoder Siemens 6FX2001-5QN25 with Profinet IO to PLC S7-1200. The...
1,109
Hi, I would like to connect an encoder to Yaskawa A1000 drive. I have a Open collector type encoder and Yaskawa need line Driver output encoder...
1,019
Hello Every one I am trying to connect the encoder with siemen's 300 plc but dont know how to do it... Could some one send me the connection of...
2,214
I'm being asked to bid a control system using Siemens S7-1500 controllers, which I don't have any experience with. The digital, analog, and...
2,672
Kindly, where can we find the Colors of the wires used inside an encoder signal cable? Any international standard for the Colors used on signals...
990