Encoder wiring to PLC
Nihopak
Apr 2021
Bangkok
I'm a beginner and not sure what to do. I want to monitor the rotation of a motor. I have a FX3U PLC and a RI58-O/100 encoder available. The encoder have 10 wires,which are A, /A, B, /B, N, /N, UB, GND, Err, +SEN according to the nameplate. It also state about 10-30 Vdc, 0.1 A. From the datasheet, this should be Put-Pull encoder? How should i connect this encoder to PLC? Any help and suggestion are very appreciate.
Reference by this datasheet
https://docs.rs-online.com/2554/0900766b813dc065.pdf
You should provide full model name to check with output type of your encoder (RS-422 or Push-Pull). But from your cable I think that it should be push-pull output then you connect any common (such as GND) to S/S pin on your PLC then connect A, B, N to your PLC follow by this wiring from this manual at page 112
https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d16601/jy997d16601q.pdf
Encoder -> FX3U
A -> X0
B -> X1
N -> X2
That wiring use for High Speed Counter C252
For additional A-, B-, N- pin are invert logic for normal they use for ensure that there are not error on signal not necessary if you don't need to use them.
Thank a lot for advices and suggestion!!
I also think it is push pull encoder, I will look for full model list as soon as possible.
I have few existing machines with Omron PLCs in them that I need to get the output from an encoder into. There are several output options...
4,059
Good evening, I am working on a project where i am using a plc DL05 with an encoder to control an axis position. My encoder signals A and B, i...
43,220
Good day I have to Wire a incremental (1024) Encoder EG7s to a Mitsubishi drive using card FR-A8APA has anyone ever wired this to any drive ...
1,391
Hi, Im a bit unsure about how to connect my SIEMENS encoder (5V TTL/RS422) To my baseunit (The light one).. I have attached a pic of how i have...
1,533
I am rebuilding a line with 2 conveyor sections, that the process speed is calculated from a rate signal from 2 high-speed counter modules. The...
1,491