We have an htl encoder connected (unipolar) to 2 inverters in parallel. After running smoothly for more than 2 months, a fault (F051) starts happening on the first inverter at a speed higher than 700 rpm.
After checking we found that the zero track is missing at high speed (we tried the speed loop without zero track and no fault happened).
We replaced the encoder by a new one, and the machine is now working ok.
Our concern is why this problem happened? And could it happen again?
The used hardware is:
Encoder, incremental, 1024 lines, 24 vdc, HTL, blind hollow shaft, connection cable, Sick (Stegmann), DGS66-HAZ0-S04
Connected to:
(x104) Inverter 18.5 kw, 37.5 A, vector, +CBP2+SLB Siemens 6SE7023-8TP60+ZG91+G42
(slot B) Inverter 11 kw, 25.5 A, motion control, +CBP2+SBP+SBP Siemens 6SE7022-6TP50+G91+C12+C13
Experience showed that usually siemens hardware does not like non-siemens parts…!
Thanks