I am in search of an EthernetIP EDS file for a GE AF-600FP drive. GE just offers a file for Devicenet. I'm assuming that an EthernetIP EDS file would be different? Thanks for any help.
-Tania
For EtherNet/IP it is more complex than that when referring to the ControlLogix. Most likely the GE drive will be setup to use the Generic EtherNet/IP module. You will need to know things like the input and output instance numbers and the associated data sizes. There should be some examples in the GE manuals or the website.
Darren
In the worst case you can create a "Stub EDS" just to allow RSLinx Classic to identify the device. Because you're very likely not using RSNetworx for EtherNet/IP to configure the GE drive, you don't need any of the Parameter Object or Bridge keywords in the EDS file.
Is RSLinx Classic browsing the GE drive and showing it as "Unknown Device" ?
If it were my system, I'd use the ControlLogix to send a "List Identity" service request to the GE drive, and use those values for Vendor, Type, Device, and Revision to create a Stub EDS using the EZ-EDS tool from the ODVA.
How would one go about getting EthernetIP to operate at higher speeds without clogging the network? I've got some I/O blocks I would like to run...
18
5,198
Hi There. I have PC to get few tags from PLC into C# windows forms application. What is the best and fastest way? I could not find Omron in...
290
Hi, I am experimenting with different devices & am battling the connection sizes. At present, have a 1734-AENT/C, 1xOB8 & 1xIB8 I have tried...
1,126
Hello All, I'm sorry that this will have been asked a thousand times, but I cannot find the specific question to search for. I am looking for...
836
Hello, I am looking for some information on converting a Flex IO (1794-ADN) which is device net to an Ethernet/Ip Flex IO module like an AENT...
430