Hello Guys,
I'm new on the forum. There was power outage on my production line some days back but after it was restored, the line did not start up.
While troubleshooting,we noticed an EXTERNAL FAULT displayed on the PLC. We eventually discovered the UPS for the PLC was not on before the power outage so we put it on and reset the PLC then the line could start up.
My question is; what are the likely causes of having an External Fault on a PLC?
And how do I fix it when it comes up.
Thank you
the eternal fault is caused by the communications dropping out before the PLC new there was a power failure.
That is what the UPS is for.
Basically the Profibus or Profinet detected a broken cable or device.
even device power failure
no problem but an external fault would be displayed
Thanks a great deal Iant. The guy I met on the job actually insists it was a 24V supply from where that was missing is the cause of the external fault. And he said, if we had RESET the main breaker for the line as many times as possible the fault will disappear.
Thanks for the input. Can you give me any material to read up on this?
Dear All We have S7-412-3H redundant system.We are facing Problem that both CPU showing External Fault. We have checked the profibus cables but...
1,195
Dear All We have SIEMENS PLC S7-412-3H redundant system having remote I/O modules connected with Profibus. During commissioning when we Power up...
2,312
Dear All, Now I have a et200s ssi module for a absolute encoder to position a roll up/down movement. But now the SF light on the card sometimes...
1,585
Please excuse me if my logic is not sound here, but I'm really reaching here... PLC is working fine. It's a 412-2 DP. We've got 2 identical...
3,120
Hello everyone, first timer here. I'm a senior electrical engineering student having a slight issue with our design project. An A-B MicroLogix...
39
15,747