For me it happened exactly how Sergei said.
Diode in parallel connected opposite.
ML1500 24VDC input, relay output, same 24VDC(10A) supply to ML.
PLC closes the output, short on 24VDC, PLC suffer due to surge (not enough supply), flash fault, resets itself and starts over and over.The fuse didn't even blink....
Didn't dare to press manually the relay, however I traced the wrong diode and since then I am telling myself I should not let the PLC to resets itself and to trap the fault.(Which I will do someday).
I will bet some money it is about some surge on the supply of the PLC.
Hook up the scope and see.