Hey guys,
I'm relatively new to PLC world.
I cannot seem to find a tag in FactoryTalk to show that my force is enabled in Studio 5000 or Logix5000.
Is this even possible?
I'm not trying to modify logic in Studio 5000 but willing to if I have to create a tag that will become true when I/O or SFC forcing is enabled.
Would it be one of Diagnostic Items? I've used @Mode and @Status to show their respective strings.
Any help would be greatly appreciated.
Best regards,
Edward
There is no native tag to do this in the PLC or FT View.
You will need to use the GSV instruction in the processor to read the status of 'Forces Enabled' and put this data into a new tag.
You will then need to display this tag on FT View to indicate whether there are Forces Enabled or not.
Tech note below:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/7730/page/1
Knowledgebase said:
Checking I/O and Module Status
Forcing status
Use a GSV instruction to access the object class MODULE, object instance <none>, attribute ForceStatus. The destination tag has to be a DINT.
Bit 0 - if 1, forces exist in the controller
Bit 1 - if 1, forces are enabled in the controller
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
198
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
44
Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
106
We are a water/wastewater plant, collecting realtime and manually entered data. We have been using FactoryTalk Historian (OSI PI) for real time...
142
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
76