Hello,

I am having an issue creating a runtime in version 6.1. This is the first time I have had this problem. In the past I have created runtime versions 6.1 for PVP6 1000 terminals. In this case I am using a PVP6 600 terminal, and the only options are 5.1 and older.

the problem is I have a terminal with 6.1 firmware, so when i try to transfer the 5.1 runtime it gives an error. It says something like connected terminal is not a valid ME format. So i need to make my runtime in 6.1 but the factory talk view software will not allow it.

what am i doing wrong here?

FactoryTalk.JPG
 
What version of Factorytalk View ME are you using? It looks like you are using Ver 6.10.
You need to use Ver 7 or 8 to be able to create a 6.1 runtime for the PVP600.
 
I am using 6.1.

Thanks for the information, that sounds exactly like something rockwell would do. Does version 8 have a substantial difference from 7?
 
The PVP600 the uses a runtime greater that ver5.1 is a new product. I think this is why the old software does not support it. As far as the differences between FTView ver 7 and 8 go most of the changes are related to adding new products and adding new features to the software.
 
You can build 5.10 version MER and it will run just fine on the 6.10 version PVP (only exception is activeX control cannot cross from v5 to v6+).
The PVP 400/600 skipped firmware version 6, which is why you don't see that as an option for your MER build.

PanelView Plus Run-time>General section
http://compatibility.rockwellautoma...x?crumb=113&toggleState=&versions=54246,54235


Is it the download that is failing? You could try copying the project over with an SD card or USB stick and see if that runs.

Otherwise, yes you will need to update to either version 7 or 8 to download over Ethernet.
If you do, go to version 8. Anyone with security user accounts will want version 8.
 

Similar Topics

Hi Guys, I developed HMI with Resolution of 1920 x 1080 in FactoryTalk View studio SE; and also use same resolution for Client Runtime PC yet...
Replies
0
Views
557
Hello I have a FactoryTalk View ME project (.apa file) and I have to make it run on our industrial PC (windows based). My question is: What I...
Replies
5
Views
2,268
Hello group, Thanks to Rockwell's infinite wisdom to change the O/S from WinCE to Win10, I have recently installed FactoryTalk View ME Version 12...
Replies
6
Views
2,404
Hello Experts, I m trying to create runtime users in FactoryTalk View ME 10.0. I m able to create runtime users, able to add them in existing...
Replies
0
Views
1,284
Good Morning , I have a customer that has an old Panelview and an obsolete 1769-L35E processer . I need to replace the HMI , and I'm changing...
Replies
2
Views
1,147
Back
Top Bottom