Fault Signal
GregPLC
Oct 2002
Milwaukee, WI
342
I have a question about getting a fault signal onto ethernet. We have the critical water systems in our plant, our well water system, our boiler feedwater system, and our RO water system. We have these new pump controllers running the pump motors...The pump controllers are a Goulds product, they're a VFD with some more advanced features than most. I would like to know, other than locally when one of these drives faults or trips out. On each drive there is a fault relay, which now we have a local light and horn tied to. I would like to SOMEHOW get this onto Ethernet. Not only that, once I get it onto the Ethernet, what sort of software would I use to see at our PC's at our desks when a drive trips out? So to simplify my question, how to I get from that 120VAC fault circuit to my PC? Using a PLC? How? I have the ability to get a PLC on the Ethernet netowrk in these locations....I would prefer to use AB stuff, but not restriced to it. And then how and what kind of software would I use on my PC to recognize this? I greatly appreciate any input on this.
Greg
Goulds is a great pump company, but they don't build their own VFDs. Find out the brand of VFD used, and contact the manufacturer. You may be able to stick an option card on the VFD to talk Modbus or Devicenet or some such.
Barring that, you can probably put Flex I/O or AutimationDirect remote I/O or Opto 22 or whatever that will give you ethernet. You will have to proram the VFD I/O to give you the critical data.
Tom Jenkins
Tom they are actually Woods drives, and they are Aquavar pump controllers ADDED to these drives which is made by Goulds. Go to the goulds site, and look at the aquavar pump controllers. I called my AB rep and he said I could use a micrologix, with a NetENI module, which will send an e-mail to our email server when an event happens.
Thanks for the help
Greg ......Tom, I'm in Milwaukee too!!! Actually up in Germantown, I reside in Milwaukee though.
If you can get VFD faults to PLC inputs, you can connet plc to pc and in PC RSLinx-OPC-Server/Read method is possible use in C++ or VB application or use some Scada appliction.
Let me start by saying I am relatively new to Siemens controllers. I have a 314 CPU with a 331-7KF02-0AB0 AI module attached. The module is...
9,864
Hi all, my MP377 connect to ET200S, let's say that a 2/4 RTD module on ET200S has input addresses 512-519, and it has a SF LED which is blinking...
2,779
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
52
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
95
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...