firmware upgradation of controlnet module
amitdas.gpil
Jan 2017
raipur
we have purchased two rockwell control net module 1756CNR/C version -25 but it not work at two controller syn condition. In one controller already existent module version 20 installed and still working but both controllers not synchronised when new module installed in other controller because lower version module require firmware up gradation.
Also i unable to upgrade 1756 CNR/B control net module 20 version. Please help me to resolve the problem
Series A & B firmware can not be upgraded to C. Why don't you install both 1756-CN2R/C? You'll need to modify the declared firmware on your RSLogix project and re-schedule the network (using RsNetworx).
Welcome to the Forum !
It sounds from your post like you are using ControlLogix Redundancy, which has very specific firmware and hardware compatibility requirements. You absolutely must follow the detailed instructions in the release notes for your specific redundancy firmware bundle.
As mentioned, the Series C hardware for the 1756-CN2R module supports only firmware written for the Series C hardware.
Likewise, older Series A and Series B modules cannot be loaded with firmware that only runs on Series C.
If this is a system that is critical enough to need ControlLogix Redundancy, I strongly recommend that you get experienced local assistance. Rockwell Automation has multiple distributors in India who can help you get in touch with the right integrator, technical support, or sales office.
I am using 2711-M3A18L1 PV300 Micro Key, FRN 4.10-4.xx which supports to DF1 driver. I need to upgrade this with DH485 driver. Can I do this...
4,931
Hi all I have tried setting up the adc on a existing pf755 with studio 32 And want the firmware to update too the firmware on the plc is 12.01...
37
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
94
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
192
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
273