Flex EX I/O

KCRider

Member
Join Date
Dec 2010
Location
CA
Posts
7
Anyone have any experience implementing Allen Bradley's Flex EX I/O systems? I have a Zone 2 application. The Flex EX will be located in a safe area and wired to instruments that are located in the field. From what I can deduce from AB's documentation, I should be okay with wiring the I/O modules directly to the field devices. Any additional input would be appreciated.
 
Hello sir
I'm not experienced on flex I/O laying;just a notice
I think, if you are working in a noisy area you should use fiber optic cable between your plc and the I/O Heads; then signals from instruments will be transmitted to the plc without any troubles
Best regards
 
I do not know what Zone 2 is, however if I assume it may be an intrinsicaly safe area, I would suggest that you get specific approval before using any devices in these areas
 
Are you suee of the area class ? Zone 2. There us a huge difference between the 2. Gas and dust.
What plc are you using? What I/O are use using? I have found some I/O is fine for class 1 div 2 installations. There are other brands of I/O out there that have better price points.
 
Thanks for your inputs. The process area where the instruments will be located is indeed a Zone 2 area. Zone 2 is equivalent to Class 1 Division 2. We're dealing with flammable gases. The main PLC is a Controllogix 1756 series processor. A Controlnet adapter is being used for connection to the Flex I/O bus. The Flex Ex I/O is located in the same enclosure as the main processor, and these components are located in a safe area (MCC room). The field wiring will be brought into the safe area and terminated on the Flex Ex I/O.
 
Do you need the intrinsically safe classified EX or have you looked at what the 1756 io is rated for. They may be rated class 1 div 2. You will have to look at that option.
 
thee intrisical areas I work at have absolutely no PLC gear inside that area.
Pneumatic Pressure reed switch
Nemur gear etc
 

Similar Topics

Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
226
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
182
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
121
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
104
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
55
Back
Top Bottom