I have two Flexlogic Processors. Both have an ethernet card installed in slot one of the expansion slots. I am trying to set a MSG instruction to read A from B. I have the MSG instruction set-up as CIP data table read. The communication path is set to "ethernet, 1, 192.168.100.200, 1, 1". The "ethernet" is the replacement for 1,1 which is the ethernet card in slot 1 of PLC A. Does not seem to be working properly, getting the connection failed error code.
Any help?
The Help file entry for CIP paths is remarkably well-written; have a look at it for details.
The basic structure of CIP paths is that they are composed of pairs of "Port, Node" numbers.
Port 1 is the backplane or virtual backplane port. Port 2 is the network port.
Slot numbers, CNet/DNet/DH+ Node numbers, and IP addresses are "Node" numbers.
Your message is making a wrong turn at the Port number of the Ethernet module, and would make another one when it gets to the destination.
Try instead:
"1, 1, 2, 192.168.100.200, 1, 0"
Yes you can produce and consume data. Just like any other Logix family controller. The 1788-ENBT is not nearly as robust as a 1756-ENBT. You can overload it if you get too carried away. The same is true when you compare the 1788-CNC to the 1756-CNB for ControlNet.
You should familiarize yourself with the connection limits of the comm modules and the FlexLogix controller itself. You can actually view the connections and activity on these devices pretty well with the embedded web pages. I also use the task monitor tool to evaluate what is going on. The task monitor is really useful for this.
I have applications running that produce/consume on both Controlnet and Ethernet IP on FlexLogix controllers it works well.
RSL
Hi guys, I have a flexlogic 5434 for home use. I'm curious if there is 3rd party software I can use to program it since I can't afford to buy...
1,355
I could do with a little help understanding how the addresses are linked. I'm having to check and probably modify an existing system which is...
2,984
Hello All, I am trying to connect my laptop to a PV 600 part number 2711-T6C5L1. I have a NET-AIC module, Flexlogic PLC and the PIC driver...
4,120
hoi; I have a problem whith reading a Tage from a PLC (AB-Flexlogix). using the ethernet/ip protocol. the message that i send to the plc is an...
4,158
102