As I understand it, separate power supplies (separate from the PLC supply and Digital I/O) are sometimes used for analog sensors to reduce noise (contactors, relays and other switched devices can cause noise on +24V DC lines). Under these circumstances, do you use the separate power supply to power the analog module as well? Or just the sensors themselves?
Also, as I understand it, isolated analog modules have the common for the analog measurement circuit separate from the common for the module power supply. These, however, may need to be tied together if there is a risk of the analog common drifting too high with respect to the module common. Under what circumstances would you want the analog measurement circuit (sensor connected to + and - inputs) to be completely floating with respect to the module/PLC power supply?
Thanks!
Try a 1meg resistor from the input to ground to bias an unconnected input to read zero. Keep in mind that a floating channel is not 0 volts but rather an undefined voltage. In order to see 0 volts,amps, a 0 volt signal (such as gnd) should be connected to the input. A pull up resistor could be used to detect a broken wire, bad card, etc.
How is floating web accumulator works ? I have a project where I will control a floating accumulator without speed trim. Input and Output rolls...
3,584
Hey Guys, I was looking for a little help on a school project. I was asked to program three pumps with two inputs, more and less. The project...
23
2,548
I need to check an axis actual travel position, and to compare it to the master travel position. To do this I have to multiply the axis travel...
2,579
We have AOIs for projects, which handle material dosing (by hand or by pipes and pumps), obviously they have comparison between setpoint and...
50
14,279
Lately there have been threads that talk about floating control, input dead bands and input filters. I want to show that these KLUDGES are not...
55
17,335