Hello all. I have a clumsy way (I think it is) of converting my rpm to feet per minute and wanted to see if someone here might have a more precise way of doing it. I ran the drive for 30 seconds and measured the displacement then divided the frequency fed-back by the drive by that value and multiplied by 2. Does anyone have a more precise way? Thank you
I just remembered, this pulling system has the motor encoder feeding back to the PF755 however, I also have an encoder direct connected to the chain pulley. I am thinking the separate encoder might be a better way calculate the fpm. Any thoughts? Thank you
Additionally, I am using the PF755 in torque mode, when speed becomes important. I have a conveyor that is run by a separate VFD and I must synchronize the speed of both drives.
You can calculate the RPM from the encoder feedback, then just multiply by the circumference of the pulley wheel to end up with inch/min, mm/min m/min dependent on your unit of measure.
If I was using a tacho with an analogue output I would agree with all the methods above, but you have an encoder that gives out pulses. So you can measure a length, drive the system that length and see how many pulses you get. The number of pulses gives the system length. Then divide the measured length by system length to get the correct distance per rev for the encoder. To make it easy I create a calibration page on an HMI.
I installed time ago a metal mesh in a 400ºC tunnel of about 30 meters with an encoder on the entrance roller, that has no traction.
I used the nominal diameter = roller diameter + mesh thickness.
A PID loop regulate the VFD frequency depending on the distance traveled, the setpoint was increasing and the difference with the encoder counter was regulated.
To avoid overflow when it reached a large number, the same amount was subtracted from both the setpoint and the counter.
When the system is stopped both quantities are initialized to zero.
The system continues to operate with great precision.
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
152
Good Morning , I have an application that I need to increase and decrease the FPM on conveyors . I have a HMI PB for increase and decrease...
26
5,228
Good Morning , Do you guys know of any tachometers ( 4-20 ma ) with a fragile soft wheel to sense FPM on a cloth belt ? I was thinking of...
2,916
I have a system with a 1000ppr hollow shaft encoder on an 8 inch diameter roller. I have the encoder connected to a hsc of my PLC. I am trying...
3,097
OK if I want to know the FPM the machine is running and I have 3 ppr on a 12” circumference wheel going to a standard DC input card on a Flexlogix...
1,793