FT View [Alarm] deleted.

tjoneill

Member
Join Date
Jul 2007
Location
Michigan
Posts
66
Hello again All. quick question I deleted the alarm pop-up screen because I already have the alarm banner on all my screens after I deleted it I’m getting a fault saying the screen is not there so I was suggested that to create another alarm screen and just have it blank, now it pops up with a blank screen every time a fault comes up. is there anyway I can get around this?
thank you again.
 
If you are talking about the default [ALARM] display then change the Display Settings and uncheck "Cannot Be Replaced" and check "Disable Initial Input Focus" and finally set you X,Y Position to a value that would be in a region that would place the display in a non-viewable screen area. I typically make these values negative numbers.
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
143
Hi all. I´ve got a little problem with my FT View SE alarm window. On my PLC program, I have 200 SINT for alarms, in which every bit is for one...
Replies
2
Views
189
This may be something obvious that I could learn if I sat down to understand the topic in detail with tutorials and manuals. But sometimes it's...
Replies
0
Views
135
Hello, we have two PC with the FT SE local application and the same project. The one PC is wrong about alarm and event log. When I open the...
Replies
2
Views
474
Is there a simple way (VBA or macro language) to acknowledge ONLY the most recent alarm? I upgraded recently all the way from RSVIEW 32 7.60 to...
Replies
4
Views
683
Back
Top Bottom