31000 - FactoryTalk View Studio Address Syntax for HMI Device Tags
Access Level: TechConnect
Date Created: 02/08/2005 12:00 AM
Last Updated: 03/30/2015 03:46 PM
Question
What syntax is used for assigning data source addresses to HMI device tags or direct references in RSView Studio?
Answer
In order to assign data source addresses to HMI device tags in FactoryTalk View Studio or assign direct references to tag connections of objects, the most common practice is to online browse for the required addresses. The communications shortcut must point to the correct controller in order to online browse.
If online browsing is not an option, the data source addresses can be entered manually. To manually enter the addresses certain addressing syntax must be followed and is summarized below.
Address Syntax for HMI Device Tags
Depending on which devices are being addressed the addressing syntax will vary. The differences in syntax reflect the differences in software used to program the controller. The ones discussed here will be devices programmable with RSLogix 5, RSLogix 500 and RSLogix 5000.
RSLogix 5
Depending on which controller device is selected the data file types that can be used with that controller will vary. The following are several data file examples and the syntax used when creating HMI device tags in RSView Studio:
Binary Data File
::[shortcut]B57:0/0
::[shortcut]BinaryDataFileDataFileNumber:Element/bit ==> if binary radix
::[shortcut]BinaryDataFileDataFileNumber:Element
Long Data File
::[shortcut]L56:0
::[shortcut]LongDataFileDataFileNumber:Element/bit ==> if binary radix
::[shortcut]LongDataFileDataFileNumber:Element
String Data File:
::[shortcut]ST61:30
::[shortcut]StringDataFileDataFileNumber:Element
Timer Data File:
::[shortcut]T59:12.ACC
::[shortcut]TimerDataFileDataFileNumber:Element
::[shortcut]TimerDataFileDataFileNumber:Element.ACC
::[shortcut]TimerDataFileDataFileNumber:Element.PRE
::[shortcut]TimerDataFileDataFileNumber:Element.EN
::[shortcut]TimerDataFileDataFileNumber:Element.TT
::[shortcut]TimerDataFileDataFileNumber:Element.DN
Float Data File:
::[shortcut]F8:20
::[shortcut]FloatDataFileDataFileNumber:Element
RSLogix 500
The syntax of addressing HMI device tags for devices in RSLogix 500 are the same as for RSLogix 5. The selection of programmable controllers vary for these two software programs, meaning that the data file types may also vary.
RSLogix 5000
The syntax of addressing HMI device tags for devices in RSLogix 5000 depends on the scope. When tags are created in RSLogix 5000 they can be created at the controller scope level (accessible to all routines), or at the program scope level (accessible to only the routines within a single program).
When a tag is created in the controller scope level the syntax for the HMI device tag address is as follows:
[shortcut]sampleTag1
When a tag is created at the program scope level the syntax for the HMI device tag address is as follows:
::[shortcut]Program
rogramName.sampleTag2
Address Syntax for Direct References
:If referencing tags directly (not HMI device tags) in the object connection tabs, the syntax is the same as above but with curly brackets.
RSLogix 5 and 500
{::[shortcut]N58:0}
RSLogix 5000
{[shortcut]sampleTag1}
or
{::[shortcut]Program
rogramName.sampleTag2}.
Address Syntax for HMI Tags
If referencing HMI tags (device or memory HMI tags) in the object connection tabs, the syntax is as follows
HMItag