Ladies & Gent's,
I am lookig to connect to an older SLC 5/02(1746-L524) unit. What should I be aware of?? I am assuming I can connect via the RS232 or Rs485 connection directly to plc unit.I have been using this unit with good success connecting to a "CLICK"plc. This will be first go round with old AB unit.

Thanks,Joe
 
Ladies & Gent's,
I am lookig to connect to an older SLC 5/02(1746-L524) unit. What should I be aware of?? I am assuming I can connect via the RS232 or Rs485 connection directly to plc unit.I have been using this unit with good success connecting to a "CLICK"plc. This will be first go round with old AB unit.

Thanks,Joe

Redlion's website has a pretty good list of Cables and Pinouts on their site. Check it out.

http://www.redlion.net/Support/Downloads/DeviceDrivers/G3/AllenBradley.html
 
Be aware that the Fixed Hardware style SLC, the 5/01 and the 5/02 do not initiate token generation for the DH485 network. So, any DH485 driver used with a 5/02 or older SLC needs to take care of that. Last time I checked, the Crimson 3.0 DH485 Master driver does not support those models. However, the techs at Red Lion may have a 'trial' driver that deals with this. It may have never been finished, but they do know about the issue and have looked at solving it.

If there is a PIC, UIC module or one of several other devices on the network to generate the first token and keep token passing going then it will work. If not, then the G3 and the 5/02 will both sit there waiting like shy school kids afraid to speak to each other.

EDIT: This document says they're still not supported:
http://www.redlion.net/Support/InfoSheet/G3-DF1DH485.pdf

But I would call them because I know they know about the issue and have at least begun the process of fixing it.:
http://www.plctalk.net/qanda/showthread.php?t=63251&page=4
http://www.plctalk.net/qanda/showthread.php?t=61599
 
Last edited:
Something to try??

I read that the SLC 5/02 plays nice with the cmore unit. I wonder of I could buy the cheapest version with 2 ports and make a simple screen list of the tags I need to use in the slc 5/02 and manipulate them with the G3 thru the other port??

Has anyone tried this ??

Joe
 
When you connect to that PLC you will need to set the Generate Initial Token setting to Yes in the driver configuration.

Thanks
Jeremy
 

Similar Topics

Hi All, As a precaution my company has been collecting copies all the HMI and PLC programs. I have recorded copies of most of our sites...
Replies
0
Views
76
While they came up quickly with a fix for the alarm date issue quickly I will have to drive around for a week or so, burning up a lot of fuel...
Replies
4
Views
290
Hey guys, hoping someone here could give me a little advice. I'm working with a CR1000-04000 in Crimson 3.1 and I was interested in adding the...
Replies
4
Views
148
From the Red Lion website, after some customer enquiries in the last week or so... Rev. March 25, 2024 [18:30] Just thought it might help a...
Replies
9
Views
298
How do you install update on Red Lion Crimson ver 3.1. Do I just need to run the exe file on the host server?
Replies
1
Views
127
Back
Top Bottom