Ge 9070
jimcav
Dec 2004
new jersey
229
Hello
Any help would be fantastic. I am using a GE 9070 plc in the rack is a innovation series controller talking to DC2000 drive. Here is the fault I get every 4 to 6 weeks. Any thoughts.
SPF.FLT.25 UC_SRTP
SRTPD I/O Driver Process Failure
Description: The SRTP I/O Driver process failed and the controller cannot
communicate with CIMPLICITY.
Suggested Action: To recover, the controller must be restarted. To restart the
controller, either
• Cycle power to the entire module, Or
• Press and release the reset button.
It is important to record events leading to the failure and contact GE.
Maybe stupid question, but does this fault display in Cimplicity?
You use the triplex driver ( SRTP ) so I assume the connection is Cimplicity - 9070 PLC and not to the Innovation controller ( that use's EGD with Cimplicity).
On the Cimplicity PC, is there any virus scanner active, or sceduled updates? that messes up communication is the experience in my factory.
Futher on, as Steve suggested, the event log in Cimplicity can bring you further.
gr.
John.
Power Supply?
Is this is an older system? I've seen with other PLCs where you get intermittent problems from noise due to aged power supply capacitors. Even an unused supply may not be ideal since some capacitors have a limited shelf life.
Good Morning, I am currently running a GE 9070 PLC. In the PLC rack there is a GE IS215UCVDH7AN card. This card is used to communicate to 5 GE DC...
2,074
Good Morning I am using a GE IS215UCVDH7AN card for my DLAN comms. I had to install my spare to get the system back up and running. I sent my...
3,203
Hi Guys, I was assigned a task to use the percentage setpoint on the HMI to have an output equivalent to 4-20ma using GE Fanuc 9070. If you have...
2,244
Hi Guys, I was given a task to configure using level setpoint to have an output of 4-20ma equivalent using GE Fanuc 9070. Is this possible? If...
2,052
Greetings to all: I am having trouble communicating to a 90-70 PLC via Ethernet using PME 8.6. I am able to ping the PLC and the HMI's...
2,071