GE Fanuc 90-30 Series PLC: Varying Register
RolandoM
Apr 2006
Monclova, Coahuila.
Hello everybody!
I am experiencing something that seems very weird to me: in one of our automatic napkin machines there is a register in which I set the time a conveyor motor will run, the thing is that no matter what value I set it will change by itself, it increases on its own, and the conveyor throw the napkins all over the place, I tried renaming it from %R004 to %R005, but it does the same, I tried to enter the program from another machine and it does it anyway.
I do not understand what is forcing this register to increase.
Any ideas and thoughts on how to solve this issue are greatly appreciated.
Regards.
Rolando.
With the GE-9030 you have to assign three (3) registers for timers and counters. This is similar to PLC-2s. Accumulated value, preset, status. If you overlap registers or use one of your registers in a different part of the logic, then this could explain why the register changes.
If you can search or do a cross reference for the specific address, then you may find the overlapping address.
The register is being written to somewhere else in the program. Based on your description, I expect that whoever wrote the program overlooked the fact that timers in a 90-30 PLC use three consecutive register addresses. If the first address on a timer is %R0004, that timer also uses %R0005 and %R0006.
Try doing an "implict" search for the register instead of an "explicit" search.
There is a simple way to avoid overlapping addresses in a 90-30. When entering the addresses, just enter "%R" instead of, for example, "%R0008". The software keeps track of the highest address actually in use for each memory type and it will pick the next available address. The technique will not fill in any gaps in the list of addresses used.
Got an old machine with a IC610CPU104 CPU. A bit of research told me this is the same as DL305 so DirectSoft from AutomationDirect should work...
2,068
Hello Does anybody have FANUC series 90-30 PLC configuration softwate? I need it . I have a big problem, Please hepl me...
1,769
Hi guys. Im a total PLC noob. i suspect a dead 331 cpu. Unable to communicate with it using the LM90 start utility. But i could on another CPU...
2,934
Hi All, I have just started using GE PLC and wish to check for some information. I was able to connect to my 90 - 70 PLC with COM1. I would...
2,909
Hi, I have gefanuc plc system 90-30 series and proficy m/c edition 5.3.My one NIU card showing LED status are BUS B and IO enable in amber...
1,491